We often use a "yard" FDC if the private fire main system only supplies building fire sprinkler systems. But if there are hydrants on the private main, we furnish individual FDC's separated from the hydrants by a check valve on each service lateral or riser.
Steve L. From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Friday, July 28, 2017 11:47 AM To: [email protected] Subject: Shared FDC Is it uncommon for a project, in this case a school campus, to have (1) yard FDC feed several buildings? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935