We often use a "yard" FDC if the private fire main system only supplies 
building fire sprinkler systems.  But if there are hydrants on the private 
main, we furnish individual FDC's separated from the hydrants by a check valve 
on each service lateral or riser.

Steve L.


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Friday, July 28, 2017 11:47 AM
To: [email protected]
Subject: Shared FDC

Is it uncommon for a project, in this case a school campus, to have (1) yard 
FDC feed several buildings?