Best disclaimer EVER Steve!!! I wish I has some laughing face emoji's to
post . 

Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590


[email protected]
www.norcalfire.com

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 
belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Thursday, August 03, 2017 11:19 AM
To: [email protected]
Subject: RE: Sprinklerforum Digest, Vol 53, Issue 3

Sure thing.  If you want to "poach" symbols from other parties, why not go
straight for the top of the food chain?:  NFPA 170, Chapter 7 ...

Good luck,
Steve Leyton
Protection Design and Consulting
San Diego, CA

The statement above is not intended to be taken seriously and does not
actually represent my own opinion nor should it be taken in any way as
directive or permission to copy any symbols or content of any kind that may
be protected by copyright or intellectual property laws, that may vary by
state.   

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Versoi, Michael
Sent: Thursday, August 03, 2017 11:11 AM
To: [email protected]
Subject: RE: Sprinklerforum Digest, Vol 53, Issue 3

Good morning, I thought I'd seen comments regarding Bluebeam a few months
ago.

I've recently downloaded Bluebeam Revu 2017 eXtreme. With no other CAD
design programs to import from, does anyone have suggestions regarding where
I can go to import (poach) Fire sprinkler symbols?
Any direction would be helpful.
Thanks


Best regards,

Michael Versoi
Fire Sprinkler General Foreman
NICET III

Siemens Industry, Inc.
Building Technologies
15900 SE Eastgate Way
Bellevue, WA. 98008
425.507.4300  Office
1.866.674.2728 Fax
425.281.7313  Mobile
24 hr Dispatch: 800-952-6348

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Tuesday, August 01, 2017 2:31 PM
To: [email protected]
Subject: Sprinklerforum Digest, Vol 53, Issue 3

Send Sprinklerforum mailing list submissions to
        [email protected]

To subscribe or unsubscribe via the World Wide Web, visit
 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

or, via email, send a message with subject or body 'help' to
        [email protected]

You can reach the person managing the list at
        [email protected]

When replying, please edit your Subject line so it is more specific than
"Re: Contents of Sprinklerforum digest..."


Today's Topics:

   1. Re: Longitudinal Bracing Question (Parsley Consulting)
   2. RE: Longitudinal Bracing Question (Hinson, Ryan)


----------------------------------------------------------------------

Message: 1
Date: Tue, 1 Aug 2017 14:18:18 -0700
From: Parsley Consulting <[email protected]>
To: [email protected],     "Kyle.Montgomery"
        <[email protected]>
Subject: Re: Longitudinal Bracing Question
Message-ID: <[email protected]>
Content-Type: text/plain; charset="utf-8"; Format="flowed"

Kyle -

Perhaps you've misinterpreted my comment, or I didn't make it very clear
that what I was categorizing as "rubbish" was not the issue that there are
net vertical reaction forces on seismic bracing.  Far from it.  What I was
referring to, and I thought I made it fairly clear, was the idea that the
lateral braces would have to "work harder" if the longitudinal braces were
configured in a way that resulted in eccentric loading of the hardware (at
either end) or the fastener to the structure.

In looking at your sketches I observed that the angle from vertical of the
brace was indicated as 45? in section view A. That would suggest to me
perhaps wrongly on my part, that what you were working with had a Wp value
that did not exceed 1.0.  I gladly concede that the net vertical reaction
forces are present regardless of the Wp and the angle of the brace.  What I
don't concede is that unless the Wp exceeds 0.5 and the angle is less than
45?, or the Wp exceeds 1.0 and the brace angle is less than 60?, those
forces require a modification of the brace arrangement.  I didn't see
anything in your sketches that suggested NVRF needed to be addressed, and if
it does under the provisions of 9.3.5.10 then it must be accounted for.

If you're installing rigid bracing it is designed to function in both
tension and compression at all times.  In fact, the L/r limits in Table
9.3.5.11.8(a)-(b)-(c) are based on the brace member being in compression and
are a means to evaluate the resistance to buckling.

I think we've exhausted this.  Thanks for the discussion.

sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> *** On 08/01/2017
12:41 PM, Kyle.Montgomery wrote:
>
> Rubbish? Challenge accepted!
>
> Of course the ?standard? configuration of seismic braces imparts a 
> vertical force on the main. A bunch of sketches would be helpful here, 
> but in lieu of, let me try to describe:
>
> In a standard configuration, the brace works in tension and 
> compression to resist the horizontal seismic forces. As the brace is 
> compressed, it imparts a vertical force downward onto the pipe; as it 
> acts in tension, it imparts a vertical force upward onto the pipe. But 
> don?t take my word for it, you helped describe it in *9.3.5.10 Net 
> Vertical Reaction Forces*, particularly where it states ?*the net 
> vertical reaction produced by the horizontal load*?. Maybe I was 
> unclear, it imparts this force as it is working (during an earthquake) 
> not in a static condition.
>
> Now in the case of the bracing configuration we?re discussing: As the 
> brace works in tension as the brace works in compression, it will 
> impart a vertical force downward and a lateral force to the right; 
> vice versa in compression. This is what I mean by making the adjacent 
> lateral braces work harder, as they would have to account for the?
> let?s call it ?net horizontal reaction force?.
>
> As far as the eccentric loads, I think you guys have a point there. I 
> think the 825 is designed to work perpendicular-to or parallel-to the 
> structure, but maybe not both conditions at the same time. My section 
> view B is kind of misleading (aka sucky), in reality the brace pipe 
> would point towards the center of the main, so it wouldn?t be as bad 
> as it looks.
>
> Sounds like I might be back to square 1.
>
> -Kyle M
>
> *From:*Sprinklerforum
> [mailto:[email protected]] *On Behalf Of 
> *Parsley Consulting
> *Sent:* Tuesday, August 01, 2017 11:51 AM
> *To:* [email protected]
> *Subject:* Re: Longitudinal Bracing Question
>
> Kyle,
>
> The photos did show up, however they're very small.
>
> From what I could discern from the photos I'd have to conclude that 
> the plan view and section view B would lead me to conclude that this 
> installation does conflict with 9.3.5.11.5, as the brace fittings at 
> the attachment to structure and attachment to the main would be 
> subject o eccentric loading for which they may not have been 
> listed/tested.
>
> When in doubt check with the good people at B-Line to see if their 
> figure 825 was tested for such an installation, not to mention the 
> figure 4A. I would doubt that it was.  It is also possible that there 
> are tension only brace fitting attachments to the structure which 
> would allow what you're showing, however I simply have not designed 
> bracing with that method enough to direct you to the correct 
> equipment. I believe this is a circumstance where you're going to have 
> to get the building structural engineer involved.
>
> I'm not sure how you're reaching the conclusion that a "standard 
> configuration" would impart any sort of vertical force on the main.
> As for the adjacent lateral braces "work harder", in as polite 
> language as I can generate - rubbish. Lateral bracing is only intended 
> to resist horizontal motion perpendicular to the axis of the pipe.
> Consider - if the detail in the "top plan view" below was for a 
> lateral brace it would still generate eccentric loads on the hardware, 
> and that would be unacceptable.
>
> sincerely,
>
> *Ken Wagoner, SET
> **Parsley Consulting
> 350 West 9th Avenue, Suite 206
> Escondido, California 92025
> **Phone 760-745-6181
> **Visit our website <http://www.parsleyconsulting.com/> *
>
> On 08/01/2017 11:06 AM, Kyle.Montgomery wrote:
>
>     Here is a picture of what I'm talking about (let me know if the
>     picture shows up):
>
>     It still maintains an appropriate angle from vertical. And it
>     still resists motion "parallel to the axis of the system piping".
>     But in doing so it will impart an additional horizontal load
>     perpendicular to the axis of the pipe (lateral) whereas a standard
>     configuration only imparts an additional vertical force. So it is
>     making the adjacent lateral braces work harder, so to speak; Is
>     that OK?
>
>     -Kyle M
>
>     -----Original Message-----
>     From: Sprinklerforum
>     [mailto:[email protected]] On Behalf
>     Of [email protected] <mailto:[email protected]>
>     Sent: Tuesday, August 01, 2017 9:18 AM
>     To: [email protected]
>     <mailto:[email protected]>
>     Subject: Re: Longitudinal Bracing Question
>
>     Thanks Ken.
>
>     I was referring to this:
>
>     *   The only "angle" which really applies in providing longitudinal
>
>     bracing is the measurement from vertical.  That angle must be at
>     least 30? and have a maximum of 90? from vertical (which is
>     perfectly horizontal, and would make the brace parallel to the pipe.
>
>     I am thinking in plan view, based on Kyle's original question, so
>     any angle from vertical would 'appear' to be parallel to the pipe.
>
>     To us Sprinkler Eccentrics, nothing is Minor
>
>     :)
>
>     Brad
>
>     Quoting Parsley Consulting <[email protected]
>     <mailto:[email protected]>>:
>
>     > Brad,
>
>     >
>
>     > While the quote from NFPA 13 is entirely correct and the brace 
> pipe
>
>     > and fittings must be in a straight line, thus avoiding eccentric
>
>     > loading on the fittings and fasteners, I did not say that the 
> brace
>
>     > has to be parallel to the pipe.
>
>     >
>
>     > What I did say was that a longitudinal brace resists horizontal
>     motion
>
>     > of the main in a direction which is parallel to that main.
>
>     >
>
>     > The angle, measured from vertical, must be at least 30? and can
>     be as
>
>     > much as 90? from vertical, which would make the brace pipe
>     parallel to
>
>     > the main, however that is not required.
>
>     >
>
>     > Minor but relevant clarification.
>
>     > *Ken Wagoner, SET
>
>     > *Parsley Consulting***
>
>     > *350 West 9th Avenue, Suite 206
>
>     > *Escondido, California 92025
>
>     > *****Phone 760-745-6181*
>
>     > Visit our website <http://www.parsleyconsulting.com/> *** On
>
>     > 08/01/2017 8:17 AM, [email protected]
>     <mailto:[email protected]> wrote:
>
>     >> From 13-2016:
>
>     >>
>
>     >> 9.3.5.11.5 All parts and fittings of a brace shall lie in a 
> straight
>
>     >> line to avoid eccentric loadings on fittings and fasteners.
>
>     >>
>
>     >> The above means, to me anyway, that it is NOT ok to kick the
>
>     >> longitudinal brace out at an angle as seen in plan view. In 
> this way
>
>     >> I think that is an angle that does matter, but Ken cleared it 
> up by
>
>     >> saying the brace pipe has to be parallel to the main pipe.
>
>     >>
>
>     >> As always, I am willing to stand to be corrected,
>
>     >>
>
>     >> Brad
>
>     >>
>
>     >> Quoting "Kyle.Montgomery" <[email protected]
>     <mailto:[email protected]>>:
>
>     >>
>
>     >>> I knew where you were going, Steve, and I agree that this is a 
> good
>
>     >>> approach. We?ve gone this route in the past, but when you get 
> to the
>
>     >>> stage of the job where I?m usually involved (closer to
>
>     >>> construction) and everyone has contracts for construction, it 
> can
>
>     >>> sometimes be contentious as far as who would provide and pay 
> for
>
>     >>> this additional engineering. So I was looking for ways to 
> control
>
>     >>> our own destiny, so to speak.
>
>     >>>
>
>     >>> Thanks for everyone?s input.
>
>     >>>
>
>     >>> -Kyle M
>
>     >>>
>
>     >>>
>
>     >>> From: Sprinklerforum
>
>     >>> [mailto:[email protected]] On 
> Behalf Of
>
>     >>> Steve Leyton
>
>     >>> Sent: Friday, July 28, 2017 3:25 PM
>
>     >>> To: [email protected]
>     <mailto:[email protected]>
>
>     >>> Subject: RE: Longitudinal Bracing Question
>
>     >>>
>
>     >>> What he said.  To clarify my earlier comment ? I did not 
> intend to
>
>     >>> suggest that you could use the trapeze values in NFPA 13 for 
> hangers
>
>     >>> and apply them to EQB anchorage.  However, we have worked with 
> our
>
>     >>> structural engineers on previous projects to design for 
> similar
>
>     >>> conditions where the shear load bearing value of the strut 
> (notice I
>
>     >>> just said strut instead of trapeze) was specified by the SEOR 
> and
>
>     >>> was adequate for the applied loads of the specific braces we 
> needed
>
>     >>> to anchor.  It CAN be done, but as Ken says, it can?t be done 
> by
>
>     >>> simply using the trapeze section moduli published in NFPA 13.
>
>     >>>
>
>     >>> Steve L.
>
>     >>> Back Peddling, CA
>
>     >>>
>
>     >>> From: Sprinklerforum
>
>     >>> [mailto:[email protected]] On 
> Behalf Of
>
>     >>> Parsley Consulting
>
>     >>> Sent: Friday, July 28, 2017 12:53 PM
>
>     >>> To:
>
>     >>>
> [email protected]<mailto:[email protected]
> <mailto:[email protected]%3Cmailto:sprinklerforum
> @lists.f>
>
>     >>> iresprinkler.org>
>
>     >>> Subject: Re: Longitudinal Bracing Question
>
>     >>>
>
>     >>> Forumites,
>
>     >>>
>
>     >>> Let's clarify a couple of items here. [All references to the
> 2016
>
>     >>> edition, and all emphasis is mine]
>
>     >>>
>
>     >>> *   Longitudinal bracing on mains must be spaced no more than 80'
>
>     >>> apart, per 9.3.5.6.1
>
>     >>>
>
>     >>> *   The distance from the end of the line and the last (or first)
>
>     >>> longitudinal brace must no exceed 40', per 9.3.5.6.
>
>     >>>    *   Your first longitudinal brace could be as much as 40' from
>
>     >>> the end of the pipe run.
>
>     >>> *   The structural components of the building must be able to
>
>     >>> resist the added seismic loads, per 9.3.5.1.2
>
>     >>>    *    This is something the building structural would have to
>
>     >>> provide, as it's not something a sprinkler contractor should 
> attempt
>
>     >>> without some training and experience in structural engineering.
>
>     >>> *   A trapeze installed per NFPA 13 guidelines is not intended to
>
>     >>> address loads other than gravity in the vertical orientation, 
> and
>
>     >>> any resistance to horizontal movement would have to be 
> designed by a
>
>     >>> structural engineer.
>
>     >>>
>
>     >>> *   As long as the brace member (pipe, rod, flat, etc) does not
>
>     >>> exceed the limits on the length imposed by tables
>
>     >>> 9.3.5.11.8(a)-(c) having it be four feet to the nearest bar 
> joist
>
>     >>> should be no problem.
>
>     >>>
>
>     >>> *   The only "angle" which really applies in providing
>
>     >>> longitudinal bracing is the measurement from vertical. That 
> angle
>
>     >>> must be at least 30? and have a maximum of 90? from vertical 
> (which
>
>     >>> is perfectly horizontal, and would make the brace parallel to 
> the
>
>     >>> pipe.
>
>     >>>
>
>     >>> The addition of another flexible coupling on the main could 
> create a
>
>     >>> further requirement for additional lateral bracing within 24"
> of the
>
>     >>> flexible coupling per 9.3.5.5.9.
>
>     >>>
>
>     >>> I hope that provides some guidance.
>
>     >>> As I am a member of the hanging and bracing committee of NFPA 
> 13,
>
>     >>> please see the disclaimer below.
>
>     >>>
>
>     >>> sincerely,
>
>     >>> Ken Wagoner, SET
>
>     >>> Parsley Consulting
>
>     >>> 350 West 9th Avenue, Suite 206
>
>     >>> Escondido, California 92025
>
>     >>> Phone 760-745-6181
>
>     >>> Visit our website<http://www.parsleyconsulting.com/>
>
>     >>>
>
>     >>> IMPORTANT NOTICE: This correspondence is not a Formal 
> Interpretation
>
>     >>> issued pursuant to NFPA Regulations. Any opinion expressed is 
> the
>
>     >>> personal opinion of the author and does not necessarily 
> represent
>
>     >>> the official position of the NFPA or its Technical Committees.
> In
>
>     >>> addition, this correspondence is neither intended, nor should 
> it be
>
>     >>> relied upon, to provide professional consultation or services
>
>     >>>
>
>     >>> It should be noted that the above is my opinion as a member of 
> the
>
>     >>> NFPA Automatic Sprinkler System Hanging and Bracing Committee 
> in
>
>     >>> accordance with the NFPA Regulations Governing Committee 
> Projects
>
>     >>> and should therefore not be considered, nor relied upon, as 
> the
>
>     >>> official position of the NFPA or its Committees
>
>     >>
>
>     >>
>
>     >>
>
>     >> _______________________________________________
>
>     >> Sprinklerforum mailing list
>
>     >> [email protected]
>     <mailto:[email protected]>
>
>     >>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>
>     >> ler.org
>
>     _______________________________________________
>
>     Sprinklerforum mailing list
>
>     [email protected]
>     <mailto:[email protected]>
>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
>
>
>
>     _______________________________________________
>
>     Sprinklerforum mailing list
>
>     [email protected]
>     <mailto:[email protected]>
>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170801/f331a8ed/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 22957 bytes
Desc: not available
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170801/f331a8ed/attachment-0001.jpg>

------------------------------

Message: 2
Date: Tue, 1 Aug 2017 21:18:48 +0000
From: "Hinson, Ryan" <[email protected]>
To: "[email protected]"
        <[email protected]>
Subject: RE: Longitudinal Bracing Question
Message-ID:
 
<mwhpr07mb31339699cf629eaf56305220c8...@mwhpr07mb3133.namprd07.prod.outlook.
com>

Content-Type: text/plain; charset="utf-8"

Ken,
I will respectfully disagree with you on this point in that I believe the
?straight line to avoid eccentric loading on fittings and fasteners? of
Section 9.3.5.11.5 is in fact a line running through the center of the
braced pipe?s long axis and acting in a coaxial line along the long axis of
the bracing member itself.  The eccentric load Section 9.3.5.11.5 is
referring to is the loading of the braced, not the braced pipe.  This brace
is not required to be located in a vertical plane passing though both of
these axes.  In many cases, this is not possible since the braced pipe may
not be running parallel to and directly below a structural member to which
it must be braced fo r spacing reasons.  Listed/approved braced piping
connections including: welded tab; Cooper B-line Figures 4A, 4LA, 4L; or
others may be rotated as necessary around the axis of the braced pipe as
long as the ?longitudinal? component of the horizontal seismic load required
for this brace can be withstood for
  all brace components as indicated in calculations.  A longitudinal brace
need not be oriented in the vertical plane as discussed above, it needs to
meet the minimum angle requirements of Figure 9.3.5.1.12.1 and those
indicated in Section 9.3.5.11.8 and Tables 9.3.5.11.8 (a-c) in the plane
where BOTH axes lie.  Eccentric loading in this plane is not allowed.  It
should be noted that any brace on a pipe is going to induce an eccentric
load on the BRACED pipe.

It is my opinion that Kyle?s proposal is correct if verified by
calculation?and if the components, namely the Figure 4LA, are turned as
necessary into the plane I discussed above.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection
Engineer O 952-656-3662 \  M 320-250-5404  \  F 952-229-2923
[email protected]  \  burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437 *Registered
in: LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems Layout

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Parsley Consulting
Sent: Tuesday, August 01, 2017 1:51 PM
To: [email protected]
Subject: Re: Longitudinal Bracing Question

Kyle,

The photos did show up, however they're very small.

>From what I could discern from the photos I'd have to conclude that the plan
view and section view B would lead me to conclude that this installation
does conflict with 9.3.5.11.5, as the brace fittings at the attachment to
structure and attachment to the main would be subject o eccentric loading
for which they may not have been listed/tested.

When in doubt check with the good people at B-Line to see if their figure
825 was tested for such an installation, not to mention the figure 4A. I
would doubt that it was.  It is also possible that there are tension only
brace fitting attachments to the structure which would allow what you're
showing, however I simply have not designed bracing with that method enough
to direct you to the correct equipment.   I believe this is a circumstance
where you're going to have to get the building structural engineer involved.

I'm not sure how you're reaching the conclusion that a "standard
configuration" would impart any sort of vertical force on the main.  As for
the adjacent lateral braces "work harder", in as polite language as I can
generate - rubbish.  Lateral bracing is only intended to resist horizontal
motion perpendicular to the axis of the pipe. Consider - if the detail in
the "top plan view" below was for a lateral brace it would still generate
eccentric loads on the hardware, and that would be unacceptable.

sincerely,
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit our website<http://www.parsleyconsulting.com/>
On 08/01/2017 11:06 AM, Kyle.Montgomery wrote:
Here is a picture of what I'm talking about (let me know if the picture
shows up):

[cid:[email protected]]

It still maintains an appropriate angle from vertical. And it still resists
motion "parallel to the axis of the system piping". But in doing so it will
impart an additional horizontal load perpendicular to the axis of the pipe
(lateral) whereas a standard configuration only imparts an additional
vertical force. So it is making the adjacent lateral braces work harder, so
to speak; Is that OK?

-Kyle M

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]<mailto:[email protected]>
Sent: Tuesday, August 01, 2017 9:18 AM
To:
[email protected]<mailto:[email protected]
kler.org>
Subject: Re: Longitudinal Bracing Question

Thanks Ken.

I was referring to this:

  *   The only "angle" which really applies in providing longitudinal
bracing is the measurement from vertical.  That angle must be at least 30?
and have a maximum of 90? from vertical (which is perfectly horizontal, and
would make the brace parallel to the pipe.

I am thinking in plan view, based on Kyle's original question, so any angle
from vertical would 'appear' to be parallel to the pipe.

To us Sprinkler Eccentrics, nothing is Minor
:)

Brad

Quoting Parsley Consulting
<[email protected]<mailto:[email protected]>>:

> Brad,
>
> While the quote from NFPA 13 is entirely correct and the brace pipe 
> and fittings must be in a straight line, thus avoiding eccentric 
> loading on the fittings and fasteners, I did not say that the brace 
> has to be parallel to the pipe.
>
> What I did say was that a longitudinal brace resists horizontal motion 
> of the main in a direction which is parallel to that main.
>
> The angle, measured from vertical, must be at least 30? and can be as 
> much as 90? from vertical, which would make the brace pipe parallel to 
> the main, however that is not required.
>
> Minor but relevant clarification.
> *Ken Wagoner, SET
> *Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, California 92025
> *****Phone 760-745-6181*
> Visit our website <http://www.parsleyconsulting.com/> *** On
> 08/01/2017 8:17 AM,
[email protected]<mailto:[email protected]> wrote:
>> From 13-2016:
>>
>> 9.3.5.11.5 All parts and fittings of a brace shall lie in a straight 
>> line to avoid eccentric loadings on fittings and fasteners.
>>
>> The above means, to me anyway, that it is NOT ok to kick the 
>> longitudinal brace out at an angle as seen in plan view. In this way 
>> I think that is an angle that does matter, but Ken cleared it up by 
>> saying the brace pipe has to be parallel to the main pipe.
>>
>> As always, I am willing to stand to be corrected,
>>
>> Brad
>>
>> Quoting "Kyle.Montgomery"
<[email protected]<mailto:[email protected]>>:
>>
>>> I knew where you were going, Steve, and I agree that this is a good 
>>> approach. We?ve gone this route in the past, but when you get to the 
>>> stage of the job where I?m usually involved (closer to
>>> construction) and everyone has contracts for construction, it can 
>>> sometimes be contentious as far as who would provide and pay for 
>>> this additional engineering. So I was looking for ways to control 
>>> our own destiny, so to speak.
>>>
>>> Thanks for everyone?s input.
>>>
>>> -Kyle M
>>>
>>>
>>> From: Sprinklerforum
>>> [mailto:[email protected]] On Behalf Of 
>>> Steve Leyton
>>> Sent: Friday, July 28, 2017 3:25 PM
>>> To:
>>> [email protected]<mailto:[email protected]
>>> iresprinkler.org>
>>> Subject: RE: Longitudinal Bracing Question
>>>
>>> What he said.  To clarify my earlier comment ? I did not intend to 
>>> suggest that you could use the trapeze values in NFPA 13 for hangers 
>>> and apply them to EQB anchorage.  However, we have worked with our 
>>> structural engineers on previous projects to design for similar 
>>> conditions where the shear load bearing value of the strut (notice I 
>>> just said strut instead of trapeze) was specified by the SEOR and 
>>> was adequate for the applied loads of the specific braces we needed 
>>> to anchor.  It CAN be done, but as Ken says, it can?t be done by 
>>> simply using the trapeze section moduli published in NFPA 13.
>>>
>>> Steve L.
>>> Back Peddling, CA
>>>
>>> From: Sprinklerforum
>>> [mailto:[email protected]] On Behalf Of 
>>> Parsley Consulting
>>> Sent: Friday, July 28, 2017 12:53 PM
>>> To:
>>> [email protected]<mailto:[email protected]
>>> <mailto:[email protected]%3Cmailto:sprinklerfor
>>> [email protected]>
>>> iresprinkler.org>
>>> Subject: Re: Longitudinal Bracing Question
>>>
>>> Forumites,
>>>
>>> Let's clarify a couple of items here. [All references to the 2016 
>>> edition, and all emphasis is mine]
>>>
>>>  *   Longitudinal bracing on mains must be spaced no more than 80'
>>> apart, per 9.3.5.6.1
>>>
>>>  *   The distance from the end of the line and the last (or first)
>>> longitudinal brace must no exceed 40', per 9.3.5.6.
>>>     *   Your first longitudinal brace could be as much as 40' from
>>> the end of the pipe run.
>>>  *   The structural components of the building must be able to
>>> resist the added seismic loads, per 9.3.5.1.2
>>>     *    This is something the building structural would have to
>>> provide, as it's not something a sprinkler contractor should attempt 
>>> without some training and experience in structural engineering.
>>>  *   A trapeze installed per NFPA 13 guidelines is not intended to
>>> address loads other than gravity in the vertical orientation, and 
>>> any resistance to horizontal movement would have to be designed by a 
>>> structural engineer.
>>>
>>>  *   As long as the brace member (pipe, rod, flat, etc) does not
>>> exceed the limits on the length imposed by tables
>>> 9.3.5.11.8(a)-(c) having it be four feet to the nearest bar joist 
>>> should be no problem.
>>>
>>>  *   The only "angle" which really applies in providing
>>> longitudinal bracing is the measurement from vertical.  That angle 
>>> must be at least 30? and have a maximum of 90? from vertical (which 
>>> is perfectly horizontal, and would make the brace parallel to the 
>>> pipe.
>>>
>>> The addition of another flexible coupling on the main could create a 
>>> further requirement for additional lateral bracing within 24" of the 
>>> flexible coupling per 9.3.5.5.9.
>>>
>>> I hope that provides some guidance.
>>> As I am a member of the hanging and bracing committee of NFPA 13, 
>>> please see the disclaimer below.
>>>
>>> sincerely,
>>> Ken Wagoner, SET
>>> Parsley Consulting
>>> 350 West 9th Avenue, Suite 206
>>> Escondido, California 92025
>>> Phone 760-745-6181
>>> Visit our website<http://www.parsleyconsulting.com/>
>>>
>>> IMPORTANT NOTICE: This correspondence is not a Formal Interpretation 
>>> issued pursuant to NFPA Regulations. Any opinion expressed is the 
>>> personal opinion of the author and does not necessarily represent 
>>> the official position of the NFPA or its Technical Committees. In 
>>> addition, this correspondence is neither intended, nor should it be 
>>> relied upon, to provide professional consultation or services
>>>
>>> It should be noted that the above is my opinion as a member of the 
>>> NFPA Automatic Sprinkler System Hanging and Bracing Committee in 
>>> accordance with the NFPA Regulations Governing Committee Projects 
>>> and should therefore not be considered, nor relied upon, as the 
>>> official position of the NFPA or its Committees
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]
>> resprinkler.org>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]
kler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]
kler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170801/a4ee150c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 22957 bytes
Desc: image001.jpg
URL:
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org
/attachments/20170801/a4ee150c/attachment.jpg>

------------------------------

Subject: Digest Footer

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


------------------------------

End of Sprinklerforum Digest, Vol 53, Issue 3
*********************************************

This message and any attachments are solely for the use of intended
recipients. The information contained herein may include trade secrets,
protected health or personal information, privileged or otherwise
confidential information. Unauthorized review, forwarding, printing,
copying, distributing, or using such information is strictly prohibited and
may be unlawful. If you are not an intended recipient, you are hereby
notified that you received this email in error, and that any review,
dissemination, distribution or copying of this email and any attachment is
strictly prohibited. If you have received this email in error, please
contact the sender and delete the message and any attachment from your
system. Thank you for your cooperation
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to