Makes sense, thanks guys. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com<http://bvssystemsinc.com/>
From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, October 12, 2017 2:40 PM To: [email protected] Subject: RE: Soffit Along a Wall Brian, I think all you have to do is comply with Table 8.8.5.1.2. 8.8.5.1.2 (3) gives you an option 'shall be permitted' that is less restrictive than the first table but can only be used when the soffit is 30" wide or less. Cliff Whitfield, SET President Fire Design, Inc. 184 Comfort Place Burnsville, NC 28714 Ph: 828-284-4772 [Description: New FDI Logo-4.jpg] [email protected]<mailto:[email protected]> www.fire-design.com<http://www.fire-design.com/> From: Sprinklerforum [mailto:[email protected]] On Behalf Of Brian Harris Sent: Thursday, October 12, 2017 11:51 AM To: [email protected]<mailto:[email protected]> Subject: Soffit Along a Wall Using extended coverage pendent heads & have a soffit/reveal that is 60" wide and runs the length of the wall and sticks down 3" from the ACT. The heads are far enough away from the edge of the soffit/reveal to through under it and reach the wall no problem. But if I'm reading things right since this soffit/reveal is along a wall I have to apply either 8.8.5.1.2 (b/c) NNFPA-13 2013) which would require heads under it as well correct? Just seems like an overkill to me. Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 ________________________________ [Avast logo]<https://www.avast.com/antivirus> This email has been checked for viruses by Avast antivirus software. www.avast.com<https://www.avast.com/antivirus>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
