WI follows the 2009ed of the IBC so 2007ed of NFPA 13 is what we follow.

Thanks,



Dewayne Martinez

Fire Protection Design Manager



*TOTAL* *Mechanical*

*Building* *Integrity*
W234 N2830 Paul Rd.
Pewaukee, WI  53072

[email protected]

Ph:  262-522-7110

Cell: 414-406-5208

*http://www.total-mechanical.com/ <http://www.total-mechanical.com/>*



[image: Consecutive Honors 2012-2017]









*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Reed A.
Roisum, SET
*Sent:* Tuesday, October 17, 2017 1:02 PM
*To:* [email protected]
*Subject:* NFPA 13 edition in Wisconsin



I am finding conflicting answers as to what edition of NFPA 13 is
applicable in Wisconsin.  It appears as though IBC 2009 is the applicable
building code, which references NFPA 13, 2007 edition.  However, I have in
my notes that NFPA 13, 2010 edition is the applicable edition for some
reason.  It may be because I believe NFPA 1, 2012 edition is the adopted
fire code and that would reference NFPA 13, 2010 edition??



Can anyone point me to something definitive for Wisconsin’s applicable
edition of NFPA 13?



Thank you.



Reed





Reed A. Roisum, SET *|* *Karges-Faulconbridge, Inc.* *|* Senior Fire
Protection Designer *|* Fargo, ND *|** direct: *701.552.9903* | **mobile:*
701.388.1352 *|* *KFIengineers.com* <http://www.kfiengineers.com>


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to