I did think about that but it’s still a 6” main which requires 3” lags……
maybe do the trap and space it at 10’ max. and use 2½” lags, only problem is
I don’t have anything to back it up down the road in the event of an issue 

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

 <mailto:[email protected]> [email protected]

 <http://www.norcalfire.com/> www.norcalfire.com

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Art Tiroly
Sent: Wednesday, October 25, 2017 10:44 AM
To: [email protected]
Subject: RE: lag bolts

 

Trapeze to spread the load?

 

 

Art Tiroly

ATCO Fire Protection/Tiroly

24400 Highland Rd CLE 44143

216-621-8899

216-570-7030 cell

 

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci Cetani 3
Sent: Wednesday, October 25, 2017 1:33 PM
To: [email protected]
Subject: RE: lag bolts

 

Sorry I should have clarified, this is for hangers not EQ bracing 

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

[email protected]

www.norcalfire.com <http://www.norcalfire.com/> 

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mitchell, Scott
Sent: Wednesday, October 25, 2017 10:24 AM
To: [email protected]
Subject: RE: lag bolts

 

Through bolt?

 

J. Scott Mitchell, PE

Senior Fire Protection Engineer

Mission Engineering

CNS Y-12 | 865-576-5258

CNS PTX | 806-477-5883

thMYA3SSEP

 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci Cetani 3
Sent: Wednesday, October 25, 2017 1:21 PM
To: [email protected]
Subject: lag bolts

 

NFPA 13 9.1.5.3.2 states that if 2½” long screws can’t be used then 2” can
but spacing can’t exceed 10’….what’s one to do if 3” lags can’t be used? We
have a 6” main and only 2½” x 12” wood joists to attach to.

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

[email protected]

www.norcalfire.com <http://www.norcalfire.com/> 

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

 


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campai
gn=sig-email&utm_content=emailclient&utm_term=icon> 

Virus-free.
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campai
gn=sig-email&utm_content=emailclient&utm_term=link> www.avast.com 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to