What are the obstructions rules concerning a fabric supply duct installed
below an ESFR system.

The RTU will shut down and collapse the duct under any of the following
conditions – Flow switch activation, heat detector and pull stations.

I don’t think it should be considered an obstruction but we have a AHJ that
is concerned that there could be up to a 60sec delay if the collapse is
triggered by the flow switch and is requiring sprinklers below unless we
can show otherwise.

Thanks,

Dewayne