As I said it's a library, open to public, well sort of. Another complicating 
factor is it's a multi-floor facility with an existing roof so we just can't 
raise the floor to create more room, even if that would help, not sure.  And 
it's historical stuff with incredibly tight HVAC requirement over 10,000's 
sqft.  So we're expecting a lot of ducts, with sprinklers under duct don't we 
force the storage down even more? . And finally, we're only writing the DB RFP, 
would actually be easier to sort this all out in detail with all disciplines 
but we ain't getting paid for that.  If we don't have viable achievable options 
for the contractor I've failed miserably.  Believe it or not a few FPE's do 
look out for you contractors. So I thought of exploring a ceiling which 
eliminates all obstructions.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]<mailto:[email protected]>
www.burnsmcd.com<http://www.burnsmcd.com/>
*Registered in: MN

Schrodinger's Smiley  :):

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield
Sent: Wednesday, November 15, 2017 4:16 PM
To: [email protected]
Subject: Re: ESFR In A Ceiling


Chris,



I have one of these projects under contract at this time.

 It's an addition to a existing stack room, the existing building

and my addition are without suspended ceilings.



I was able to have the lights spaced as not to be an obstruction but

had to have esfr's under the ductwork.



It's a stack room, why would someone want a more finished look.........LOL



Mike

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Cahill, Christopher 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, November 15, 2017 4:42 PM
To: 
[email protected]<mailto:[email protected]>
Subject: ESFR In A Ceiling


Can anyone point me to a k25 ESFR in chrome or white and associated deep 
escutcheon so I can put them in a ceiling like an ordinary k5.6 in an office?  
I have a library archives stack room with mobile shelving units where ESFR k25 
is required (just accept this is the required design). I'm thinking with the 
structure, lights, HVAC, etc it might be better to put a ceiling in and get rid 
of all the obstructions.  Looking around I'm not sure I can find something with 
a more finished look.



Chris Cahill, PE*

Associate Fire Protection Engineer

Burns & McDonnell

Phone:  952.656.3652

Fax:  952.229.2923

[email protected]<mailto:[email protected]>

www.burnsmcd.com<http://www.burnsmcd.com/>