They just seemed backwards Ken.
Then I read Appendix E.
I had made the mistake of thinking it was all about total weight from the zoi, so smaller pipe would be less weight, and after the adjustments to load ratings- if 4" at 40' is 'under', 2.5" at 40' would be 'underer'. My only conclusion is that I a ashamed of myself for assuming it was all about total weight and nothing more.
Thanks Dude, Brad.

Quoting Parsley Consulting <[email protected]>:

Brad,

I'm not following your conclusions with the information you've provided.

Remember that the values in Tables 9.3.5.5(a)-(l) are maximum allowable loads for various types of pipe and spacing of the lateral braces from each other.

Consider that if you were bracing 4" schedule 10 pipe, and the lateral braces were spaced greater than 35' apart, but less than 40' apart the maximum allowable load 769#.  It is true that the maximum allowable load if the lateral braces were spaced closer together, for example greater than 25' but less than 30', the value from Table 9.3.5.5.2(a) for the maximum allowable Fpw in the ZOI is no 1,071#.

You're of course welcome to tentatively space your lateral braces at the maximum spacing of 40' per 9.3.5.5.2.2.  The very next paragraph, 9.3.5.5.2.3 mandates that the Fpw cannot exceed the allowable loads in the tables.  As a result of that consideration you may indeed have to respace the lateral bracing to be closer together in order to have the resulting ZOI Fpw not exceed the allowable load.

The tables aren't backwards by any means.  The values for, say 2½" pipe are lower than that for 4" piping - _*at the same brace spacing*_ - because when the strength of materials calculations are completed it's obvious that the smaller pipe is susceptible to significant damage at much lower values.

One very valuable illustration for what these tables are addressing is that they take into consideration the allowable load between the lateral braces depending on their spacing.

As I am a member of the hanging and bracing committee please see the disclaimer below.

sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> ***
On 11/27/2017 11:16 AM, [email protected] wrote:
Thanks Ken, yes, I understand this.
And I understand the zone of influence and so forth.
But these Max Load Tables threw me when I got into them more- they seemed 'backwards'. In terms of calcing the loads in the Z.O.I., the 40' spacing will be greater than the 20' spacing. But I read Appendix E and figured it had to due with pipe deflection, not just total weight. So If these tables apply I cannot 'tentatively' space lateral braces at 40'. And I cannot know my calc for 4" main at 40' works and assume my 2.5" main at 40' works because it is 'less demanding'.
I hope this makes sense.

thanks again,
Brad


*IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should it be relied upon, to provide professional consultation or services**
**
**It should be noted that the above is my opinion as a member of the NFPA Automatic Sprinkler System Hanging and Bracing Committee in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the NFPA or its Committees*