If I'm understanding your description and question properly you are
covering about 116-117 sqft of floor area if one considers the 1'8" rise at
the tip of the tooth an obstruction, which I would, and your "throw
distance" along the slope is at 0-360 degrees=7.5'/90 degrees=7.0'/180
degrees=7.5 degrees/270 degrees=1.0'. That puts you within coverage rules
for OH, and throw range rules for SS sprinklers.

On Thu, Nov 30, 2017 at 8:33 AM, Michael Hill <[email protected]> wrote:

> I am working on a firing range that is going to have a saw-tooth type
> ceiling installed. I have a question about determining maximum protection
> area per sprinkler.
>
>
>
> The vertical portion is 1’-8” tall with the distance from the high point
> to the low point being 8’-0”, measured along the slope. Sprinklers need to
> be spaced close to the vertical portion of the ceiling, to protect them
> from stray projectiles. The sprinkler will end up being about 7’-0” from
> the low point of the ceiling, measured along the slope. The sprinklers are
> about 8’-0” apart, but with a 1’-8” vertical portion of the ceiling between
> them. Sprinklers are spaced 15’-0” apart along the branchline. See attached
> sketch (if it came through).
>
>
>
> Would the spacing be 15’ x 8’ or would it be 15’ x 14’?
>
>
>
> I feel it should be 15’ x 14’ as any individual sprinkler needs to cover
> 7’-0” in one direction, measured along the slope. I feel the vertical
> portion of the ceiling is an obstruction and can almost been interpreted as
> a wall that extends to the floor. I also thought I needed to increase my
> design area for sloped ceiling for this situation, but have since been
> shown the commentary in the handbook that explains why it is not required
> for saw-toothed ceilings. Maybe I am wrong about the spacing as well.
>
>
>
>
>
>
>
>
>
> Mike Hill
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>


-- 
Ron Greenman

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to