I'm still trying to wrap my head around this. For the most part I don't this
the area above the floating ceilings can be classified as a concealed space
from the rules in 13 (2016). All the ceiling are less than 12"  below a
concrete deck, but I don't know why that would exclude sprinkler above the
ceiling.

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Taylor Schumacher
Sent: Thursday, December 14, 2017 9:04 AM
To: [email protected]
Subject: RE: Floating Ceilings

 

Buzz through 8.15, especially 8.15.22, for the other areas. But, if your
sprinkler is within the allowable distance to the ceiling, I can't think of
a reason why you would need protection above.

 

 

Taylor Schumacher, CET

 <http://www.j-berd.com/> Security Fire Sprinkler

P.O. BOX 7308 | St. Cloud, MN 56302-7308

3308 Southway Drive | St. Cloud, MN 56301

Office: 320.656.0847 |  <mailto:[email protected]>
[email protected]

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jerry Van Kolken
Sent: Thursday, December 14, 2017 10:49 AM
To: [email protected]
Subject: RE: Floating Ceilings

 

In most case yes. 

 

Jerry Van Kolken

Millennium Fire Protection

(760) 722-2722

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Taylor Schumacher
Sent: Thursday, December 14, 2017 4:30 AM
To: [email protected]
Subject: RE: Floating Ceilings

 

Can the pendent be less than 12" from the main ceiling?

 

 

Taylor Schumacher, CET

 <http://www.j-berd.com/> Security Fire Sprinkler

P.O. BOX 7308 | St. Cloud, MN 56302-7308

3308 Southway Drive | St. Cloud, MN 56301

Office: 320.656.0847 |  <mailto:[email protected]>
[email protected]

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jerry Van Kolken
Sent: Wednesday, December 13, 2017 6:03 PM
To: [email protected]
Subject: Floating Ceilings

 

I have some floating ceilings that will possible have a space greater than
6" from the framing to the deck above. On 2 sides they are roughly 6" from a
soffit and ranged from 18" to 48" from the far wall. It seems very
impractical to install sprinkler above these ceiling, but I'm not sure what
exclusions would allow me to not have to install the sprinkler above this
ceiling arrangement. The ceilings are of limited combustibility under a
concrete deck.

 

Any suggestions would be appreciated.

 

Thanks

 

 