The cut sheet you mention is actually pulling from '13 section 8.4.6.3.1 <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon> Virus-free. www.avast.com <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link> <#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
On Mon, Feb 5, 2018 at 12:59 PM, Brian Harris <bhar...@bvssystemsinc.com> wrote: > Quick question. I have an ESFR application and the roof structure is made > out of concrete tee’s, 24” deep from inside face to bottom of stem. Looking > over the cut sheet for the Tyco ESFR-25 Pendent it states that any solid > member over 12” deep you need to install sprinklers in each channel formed > by the structural members. When looking at the Viking ESFR VK510 (25.2K) I > don’t see those same parameters so I guess I would then go back to NFPA-13 > (2013) and install per 8.12.4.1.3 correct? > > > > *Brian Harris, CET* > > BVS Systems Inc. > > Design Manager > > bvssystemsinc.com > > Phone: 704.896.9989 <(704)%20896-9989> > > Fax: 704.896.1935 <(704)%20896-1935> > > > > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > >