The cut sheet you mention is actually pulling from '13 section 8.4.6.3.1

<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=icon>
Virus-free.
www.avast.com
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail&utm_term=link>
<#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>

On Mon, Feb 5, 2018 at 12:59 PM, Brian Harris <bhar...@bvssystemsinc.com>
wrote:

> Quick question. I have an ESFR application and the roof structure is made
> out of concrete tee’s, 24” deep from inside face to bottom of stem. Looking
> over the cut sheet for the Tyco ESFR-25 Pendent it states that any solid
> member over 12” deep you need to install sprinklers in each channel formed
> by the structural members. When looking at the Viking ESFR VK510 (25.2K) I
> don’t see those same parameters so I guess I would then go back to NFPA-13
> (2013) and install per 8.12.4.1.3 correct?
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> Design Manager
>
> bvssystemsinc.com
>
> Phone: 704.896.9989 <(704)%20896-9989>
>
> Fax: 704.896.1935 <(704)%20896-1935>
>
>
>