If FM or NFPA says we need a 24" deep draft curtain to separate ESFR/Storage 
sprinklers from non-storage sprinklers, but we have pendent sprinkler located 
just below the 22" deep Tees, is the curtain still needed if those tee run 
parallel to the proposed draft curtain?  Or is the intent to provide 24" a 
draft stop BELOW the level of sprinklers (not just below the ceiling)?