Here's one for you all: If FM or NFPA says we need a 24" deep draft curtain to separate ESFR/Storage sprinklers from non-storage sprinklers, but we have pendent sprinkler located just below the 22" deep Tees, is the curtain still needed if those tee run parallel to the proposed draft curtain? Or is the intent to provide 24" a draft stop BELOW the level of sprinklers (not just below the ceiling)?
Mark Sornsin Sr. Fire Protection Engineer Summit Companies Direct:701-499-1391 Cell:701-526-8585 The information transmitted, including attachments, is intended only for the person(s) or entity to which it is addressed and may contain confidential and/or privileged material. Any review, retransmission, dissemination or other use of, or taking of any action in reliance upon this information by persons or entities other than the intended recipient is prohibited. If you received this in error, please contact the sender and destroy any copies of this information. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org