I would recommend using standard response sprinklers (Section 8.3.3 Thermal Sensitivity),
On Mon, Feb 26, 2018 at 9:08 AM, John Irwin <john.ir...@dynafire.com> wrote: > So here’s the situation … We are replacing a large section of corroded > piping in the sanctuary of a church. In doing so we will be installing 156 > new sprinklers. We have ordered quick response for this light hazard area. > However, there is an additional 90 sprinklers in this same compartment that > are standard response. > > > > Did we order the wrong sprinklers, or do we now have to change out the 90 > standard response with new quick response? > > > > I can’t find a code reference to specifically address this situation. > > > > We are in 2013 CODE. > > > > John Irwin > > Fire Sprinkler Specialist > > DynaFire, Inc. > > 727-282-9243 – Cell > > > > *“A customer is the most important visitor on our premises. He is not > dependent on us. We are dependent on him. He is not an interruption on our > work. He is the purpose of it. He is not an outsider on our business. He is > a part of it. We are not doing him a favour by serving him. He is doing us > a favour by giving us an opportunity to do so.”* > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: <http://lists.firesprinkler.org/private.cgi/ > sprinklerforum-firesprinkler.org/attachments/20180226/ > 20c06811/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180226/87286942/attachment.html> _______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org