I would recommend using standard response sprinklers (Section 8.3.3 Thermal
Sensitivity),

On Mon, Feb 26, 2018 at 9:08 AM, John Irwin <john.ir...@dynafire.com> wrote:

> So here’s the situation … We are replacing a large section of corroded
> piping in the sanctuary of a church. In doing so we will be installing 156
> new sprinklers. We have ordered quick response for this light hazard area.
> However, there is an additional 90 sprinklers in this same compartment that
> are standard response.
>
>
>
> Did we order the wrong sprinklers, or do we now have to change out the 90
> standard response with new quick response?
>
>
>
> I can’t find a code reference to specifically address this situation.
>
>
>
> We are in 2013 CODE.
>
>
>
> John Irwin
>
> Fire Sprinkler Specialist
>
> DynaFire, Inc.
>
> 727-282-9243 – Cell
>
>
>
> *“A customer is the most important visitor on our premises. He is not
> dependent on us. We are dependent on him. He is not an interruption on our
> work. He is the purpose of it. He is not an outsider on our business. He is
> a part of it. We are not doing him a favour by serving him. He is doing us
> a favour by giving us an opportunity to do so.”*
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://lists.firesprinkler.org/private.cgi/
> sprinklerforum-firesprinkler.org/attachments/20180226/
> 20c06811/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180226/87286942/attachment.html>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to