Here is a nice little look at 'superior pattern for residential': https://dps.mn.gov/divisions/sfm/programs-services/Documents/Quick%20Response%20Newleter/QR0809SprayPatternsResidential.pdf
And since this is an existing system in a new "loft" with regard to calculations I thought it would be interesting to work it backwards by doing a source calc (what density will it deliver) by calcing 1500 s.f. and 3000 s.f. and plotting that on the density/area graphs and see where it lands--- Then you could say things like, "this loft is light hazard and a half", or "This loft is OH2.5", etc. :) Brad -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Friday, March 16, 2018 8:06 PM To: [email protected] Subject: Re: [EXTERNAL] RE: Existing 3/4" outlets It's a head scratcher for sure. One of those Occupancy Classifications that's hard to pin down with just words, then apply all the rules that go along with that vagueness. B. Quoting "Kyle.Montgomery" <[email protected]>: > Well, it does give us something to think about. I wonder, though, does > the residential sprinkler head's ability to provide "better control > than spray sprinklers in residential occupancies" (quoted from NFPA > 13) necessarily mean that the commercial QR head is inadequate for the > job? I submit that it is not, due to the fact that NFPA 13 still > allows it's use in this scenario. I mean, a Lexus is better than a > Toyota, but they'll both get you to work every day. > > If I were the engineer of record, I might require residential > sprinklers in the spec. But, if I were the installing contractor in > this case (and not otherwise hand-tied by the spec) I think I would > install the most economical QR sprinkler, be code-compliant, and call > it a day. Or, maybe not change a thing if the existing heads are > already QR. > > -Kyle M > > -----Original Message----- > From: Sprinklerforum > [mailto:[email protected]] On Behalf Of > cw bamford > Sent: Friday, March 16, 2018 4:39 PM > To: [email protected] > Subject: Re: [EXTERNAL] RE: Existing 3/4" outlets > > "the right Sprinkler Head for the right job" > in a Hallway of a hotel or apartment building most AHJ's will accept a > residential head---or you can use a light hazard head..... > > Residential Heads----react fast --- high wall wetting---- Prevent > Flashover > --- and give opportunity > to Exit..... usually .05 gpm /sqft > > Light Hazard Quick Response .10 gpm /sqft a lot more water ....but is > it Superior? ...for Life Safety? > > we started off with THIS quote > "light hazard residential exposed “loft” space" > hmmmm what is that? a Live Work unit? a painter? potter with kiln? > or just a residence? > > Chuck Bamford SET > > > On Fri, Mar 16, 2018 at 1:04 PM, Kyle.Montgomery > <[email protected]> > wrote: > >> Is that the general consensus? I've never really thought of >> residential heads being far superior to commercial QR heads. I mean, >> we use residential sprinklers all the time, but primarily because >> they are advantageous to us in the types of buildings we are >> installing (4-head calc, better extended coverage options, etc.). I >> guess I've always considered a residential system to be more lenient >> (i.e. less water flow and pressure required) and thus a "lower" level >> of protection than your standard light hazard system. >> >> If residential heads are actually providing a "higher" level of >> protection, then why is it that quick response commercial heads can >> be used in both residential and commercial occupancies, but that >> residential heads may only be used in residential occupancies? >> >> -Kyle M >> >> -----Original Message----- >> From: Sprinklerforum [mailto:[email protected]. >> org] On Behalf Of [email protected] >> Sent: Friday, March 16, 2018 11:17 AM >> To: [email protected] >> Subject: Re: [EXTERNAL] RE: Existing 3/4" outlets >> >> Kyle, if there is even a whiff of Residential about the occupancy the >> listed res should be used because, along with the quick response, res >> heads have a superior pattern, wetting not only the floor but high up >> on the walls too (curtains, bookshelves, the curio cabinets full of >> Russian Shadow Boxes, etc.) >> >> Brad. >> >> Quoting "Kyle.Montgomery" <[email protected]>: >> >> > Do you NEED residential heads, or can you just use any >> > quick-response head? Even if it over-discharges, I wouldn't expect >> > that to be a problem for the calcs since it was originally >> designed for OH 2. >> > >> > Why do you even need to change the heads? Are the existing K-8 >> > heads standard response? >> > >> > -Kyle M >> > >> > -----Original Message----- >> > From: Sprinklerforum >> > [mailto:[email protected]] On Behalf >> > Of Dewayne Martinez >> > Sent: Friday, March 16, 2018 9:46 AM >> > To: [email protected] >> > Cc: Dewayne Martinez <[email protected]> >> > Subject: [EXTERNAL] RE: Existing 3/4" outlets >> > >> > That’s a thought.....The problem is the original shell with 3/4" >> > uprights with a pipe centerline of 12" below deck. No residential >> > uprights in 3/4" >> > and I thought residential pendant heads are not listed to be >> > installed exposed? >> > >> > Dewayne Martinez >> > Fire Protection Design Manager >> > >> > TOTAL Mechanical >> > Building Integrity >> > >> > W234 N2830 Paul Rd. >> > Pewaukee, WI 53072 >> > [email protected] >> > Ph: 262-522-7110 >> > Cell: 414-406-5208 >> > https://urldefense.proofpoint.com/v2/url?u=http-3A__www.total-2Dmec >> > h >> > an >> > ical.com_&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOy >> > S >> > 3b >> > n8etxB7nLN8OBJwQd9A&m=QgdEeClG--ixhAlrzYXkB9w1GVgwdnHkcfh2xsZlbVU&s >> > = >> > m9 niRfDrj2QzVwiLzgS0z9PaTLR67E2v662JDvbdOzA&e= >> > >> > >> > -----Original Message----- >> > From: Sprinklerforum >> > <[email protected]> On Behalf Of Mike >> > B Morey >> > Sent: Friday, March 16, 2018 9:57 AM >> > To: [email protected] >> > Subject: Re: Existing 3/4" outlets >> > >> > You say bushing, I say sprinkler head extension less than 2" per 6.4.8? >> > >> > >> > Mike Morey >> > CFPS 3229 • NICET S.E.T. 123677 >> > Project Manager • Fire Protection Group Shambaugh & Son, LP an >> > EMCOR Company >> > 7614 Opportunity Drive • Fort Wayne, IN • 46825 direct 260.487.7824 >> > / cell >> > 260.417.0625 / fax 260.487.7991 email [email protected] >> > >> > >> > >> > >> > >> > >> > >> > From: Dewayne Martinez <[email protected]> >> > To: [email protected] >> > Cc: Dewayne Martinez <[email protected]> >> > Date: 03/15/2018 06:43 PM >> > Subject: Existing 3/4" outlets >> > Sent by: "Sprinklerforum" >> > <[email protected]> >> > >> > >> > >> > >> > BE ADVISED - This email originated outside EMCOR. >> > >> > >> > I have a project that was originally designed as a OH II space that >> > will now be turned into a light hazard residential exposed “loft” >> > space. The existing ¾” K8.0 sprinklers over discharge like crazy. >> > Can I bush the 3/4'” >> > outlets down to ½” to use K5.6 sprinklers? If not any suggestions? >> > >> > >> > >> > Dewayne Martinez >> > >> > Fire Protection Design Manager >> > >> > >> > >> > *TOTAL* *Mechanical* >> > >> > *Building* *Integrity* >> > >> > >> > W234 N2830 Paul Rd. >> > Pewaukee, WI 53072 >> > >> > [email protected] >> > >> > Ph: 262-522-7110 >> > >> > Cell: 414-406-5208 >> > >> > https://urldefense.proofpoint.com/v2/url?u=http-3A__www.total-2Dmec >> > h >> > an >> > ical.com_&d=DwIGaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uu >> > Y >> > OS >> > JoclVWgSRO8Nq6TDdsg&m=B1gjGjTnf7-Ej9T8PcnuSRVFemMqu2U1aEPDQxrOPHo&s >> > = Ru Z6bsVtOYaDGrG_UfPQiu-9SlgO6obtB79V-_fi8X8&e= >> > >> > >> > [image: Consecutive Honors 2012-2017] >> > -------------- next part -------------- An HTML attachment was >> > scrubbed... >> > URL: < >> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprin >> > k >> > le >> > r.org_private.cgi_sprinklerforum-2Dfiresprinkler.org_attachments_20 >> > 1 >> > 80 >> > 315_41e14879_attachment.html&d=DwIGaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4 >> > t >> > 2h >> > rRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=B1gjGjTnf7-Ej9T8PcnuSRVFem >> > M qu >> > 2U1aEPDQxrOPHo&s=6cdt-sQIacSh7qM78kH-MF2ygexAPpze5AppEvB6NWY&e= >> >> >> > -------------- next part -------------- A non-text attachment was >> > scrubbed... >> > Name: image001.jpg >> > Type: image/jpeg >> > Size: 8202 bytes >> > Desc: not available >> > URL: < >> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprin >> > k >> > le >> > r.org_private.cgi_sprinklerforum-2Dfiresprinkler.org_attachments_20 >> > 1 >> > 80 >> > 315_41e14879_attachment.jpg&d=DwIGaQ&c=GKdB6-XpYq_0W-WluyVHtw&r=z4t >> > 2 >> > hr >> > RBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=B1gjGjTnf7-Ej9T8PcnuSRVFemM >> > q >> > u2 U1aEPDQxrOPHo&s=b2vPc9rxHD40k3ZkHc9JYKjhqeCngJKY6_kzQNoy5EM&e= >> >> >> > _______________________________________________ >> > Sprinklerforum mailing list >> > [email protected] >> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprin >> > k >> > le >> > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=GK >> > d >> > B6 >> > -XpYq_0W-WluyVHtw&r=z4t2hrRBa-JsS06T4X_uuYOSJoclVWgSRO8Nq6TDdsg&m=B >> > 1 >> > gj >> > GjTnf7-Ej9T8PcnuSRVFemMqu2U1aEPDQxrOPHo&s=eLw-8Ymu6_DIM_XseIvcGIrkA >> > 6 >> > vC >> > iJ168TukvdOr5j4&e= >> > >> > >> > >> > >> > This message is for the named person's use only. It may contain >> > confidential, proprietary or legally privileged information. No >> > confidentiality or privilege is waived or lost by any >> > mistransmission. If you receive this message in error, please >> > immediately delete it and all copies of it from your system, >> > destroy any hard copies of it and notify the sender. You must not, >> > directly or indirectly, use, disclose, distribute, print, or copy >> > any part of this message if you are not the intended recipient. >> > -------------- next part -------------- An HTML attachment was >> > scrubbed... >> > URL: >> > <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firespri >> > n >> > kl >> > er.org_private.cgi_sprinklerforum-2Dfiresprinkler.org_attachments_2 >> > 0 >> > 18 >> > 0316_cde5a3c9_attachment.html&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z >> > _ >> > 2A >> > 85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=QgdEeClG--ixhAlrzYXkB9w1G >> > V gw >> > dnHkcfh2xsZlbVU&s=x4QRiSBmHyPdazXzYKVGEd30oSGMPM5DJJVhe6_wAGI&e=> >> > -------------- next part -------------- A non-text attachment was >> > scrubbed... >> > Name: not available >> > Type: image/jpeg >> > Size: 47302 bytes >> > Desc: not available >> > URL: >> > <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firespri >> > n >> > kl >> > er.org_private.cgi_sprinklerforum-2Dfiresprinkler.org_attachments_2 >> > 0 >> > 18 >> > 0316_cde5a3c9_attachment.jpe&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_ >> > 2 >> > A8 >> > 5VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=QgdEeClG--ixhAlrzYXkB9w1GV >> > g wd >> > nHkcfh2xsZlbVU&s=jqJ7COEDSRD_wOSQxBg6jnTuAHVGNNzUfm0HMFRvdmo&e=> >> > _______________________________________________ >> > Sprinklerforum mailing list >> > [email protected] >> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprin >> > k >> > le >> > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn >> > 3 >> > mZ >> > QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Q >> > g >> > dE >> > eClG--ixhAlrzYXkB9w1GVgwdnHkcfh2xsZlbVU&s=-TCa1XXsnA51Bra_kuZbQd5r- >> > y >> > 8W tLBBnQUb8oFJF54&e= >> > _______________________________________________ >> > Sprinklerforum mailing list >> > [email protected] >> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprin >> > k >> > le >> > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn >> > 3 >> > mZ >> > QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Q >> > g >> > dE >> > eClG--ixhAlrzYXkB9w1GVgwdnHkcfh2xsZlbVU&s=-TCa1XXsnA51Bra_kuZbQd5r- >> > y >> > 8W tLBBnQUb8oFJF54&e= >> > _______________________________________________ >> > Sprinklerforum mailing list >> > [email protected] >> > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprin >> > k >> > le >> > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn >> > 3 >> > mZ >> > QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=- >> > 6 >> > 8L >> > 2iHNkp1wPECR_Wf3hTeWDuAgQIxrVhRD_rxtzis&s=KIAIFCTT8KQLRZcJBiWKoZB7v >> > a >> > CR >> > NCIDn-iuB6ezq3Y&e= >> >> >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists. >> firesprinkler.org_listinfo.cgi_sprinklerforum- >> 2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_ >> 2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=-68L2iHNkp1wPECR_ >> Wf3hTeWDuAgQIxrVhRD_rxtzis&s=KIAIFCTT8KQLRZcJBiWKoZB7vaCRNC >> IDn-iuB6ezq3Y&e= >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=vDF6Y_Lm1nRaxayfHTWQ2U6rF8vVGhicAOjHWjxR1WU&s=NoOL9NmJjkIJzgzeo7Q52K0UoomdP0X5UH_CicnE3n8&e=. >> org >> > -------------- next part -------------- An HTML attachment was > scrubbed... > URL: > <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkl > er.org_private.cgi_sprinklerforum-2Dfiresprinkler.org_attachments_2018 > 0316_ba4a1f03_attachment.html&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A > 85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=vDF6Y_Lm1nRaxayfHTWQ2U6rF8vV > GhicAOjHWjxR1WU&s=CEWbw6iORkmI89Z5Yhme4rXjAx8_Ibcd-Wc-7-W7HMk&e=> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle > r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZ > QLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=vDF6 > Y_Lm1nRaxayfHTWQ2U6rF8vVGhicAOjHWjxR1WU&s=h7ih70x3ugE5CGJpuTf_eWuNSsCL > CWiFFjySTlAsZYg&e= _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org