Hello all!  Long time listener, first time caller.

NFPA 13 (2016 version) 17.2.2.6.1 reads "In-rack sprinklers shall be installed 
at the first tier level at or above one-half of the storage height."  Could you 
confirm 17.2.2.6.1 doesn't REQUIRE in-rack sprinklers, and only identifies HOW 
to install in-rack sprinklers when they are required by Table 17.2.2.1?   Why 
is the wording different than the In-Rack section for ESFR (17.2.3.4.1), which 
reads "Where required by Table 17.2.3.1, in-rack sprinklers shall be installed 
at the first tier level at or above one-half of the storage height."?

Thank you!

Drew Lange