When you say that you tweak it to find the actual demand – does your software not tell you the psi input required to supply the hose demand you request at the standpipe outlets? I usually see ‘required pressure’ as an output of the software no matter what the input is.
Matt From: Sprinklerforum <[email protected]> On Behalf Of Dewayne Martinez Sent: Tuesday, April 17, 2018 6:02 AM To: [email protected] Cc: Dewayne Martinez <[email protected]> Subject: Supply calculation for manual-wet standpipe One of my free lancers sent me a supply calculation for a manual wet standpipe. I have always put in a “pumper connection” supply at the FDC, did a demand calc and tweaked it until I ended up with a zero pound cushion to see what was really required. His way looks to be good. Have I been taking the hard way around to solve what PSI is required at the FDC? Thanks, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI 53072 [email protected]<mailto:[email protected]> Ph: 262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com/ [Consecutive Honors 2012-2017]