NFPA 13, 2016 edition addresses the omission of sprinklers for elevators in 
both 8.15.5.3 and 8.15.5.6. (see below)

Section 8.15.5.6 only allows sprinklers to be omitted at the top of a hoistway 
for passenger elevators.  However, as written, 8.15.5.3 allows sprinklers to be 
omitted, including at the top of the hoistway, for any type of elevator 
including freight elevators.

Just want to make sure that I am reading this correctly that NFPA 13 allows no 
sprinklers for traction freight elevators if all the items in 8.15.5.3 are met 
even for freight elevators?

Looking at the 2013 ROP/ROC, I can't tell if there was intent to allow the 
omission for freight elevators or not.

Thoughts?

Pete Larrimer
VA

*****************

8.15.5.3 Automatic fire sprinklers shall not be required in elevator machine 
rooms, elevator
machinery spaces, control spaces, or hoistways of traction elevators installed 
in accordance
with the applicable provisions in NFPA 101, or the applicable building code, 
where all of the
following conditions are met:
(1) The elevator machine room, machinery space, control room, control space, or 
hoistway of
traction elevator is dedicated to elevator equipment only.
(2) The elevator machine room, machine room, machinery space, control room, 
control
space, or hoistway of traction elevators are protected by smoke detectors, or 
other automatic
fire detection, installed in accordance with NFPA 72.
(3) The elevator machinery space, control room, control space, or hoistway of 
traction elevators
is separated from the remainder of the building by walls and floor/ceiling or 
roof/
ceiling assemblies having a fire resistance rating of not less than that 
specified by the
applicable building code.
(4) No materials unrelated to elevator equipment are permitted to be stored in 
elevator
machine rooms, machinery spaces, control rooms, control spaces, or hoistways of 
traction
elevators.
(5) The elevator machinery is not of the hydraulic type.


8.15.5.6 The sprinkler required at the top of the elevator hoistway by 8.15.5.5 
shall not be
required where the hoistway for passenger elevators is noncombustible or 
limited-combustible
and the car enclosure materials meet the requirements of ASME A17.1, Safety 
Code for Elevators
and Escalators.

******************