With the suction control closed, and everything downstream tight, whether or not the checks were fully seated would not matter, right?

Brad

Quoting "Micah Davis, SET" <[email protected]>:

100% above ground.


Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV    Dynamic Fire Designs

Mail: [email protected]
Mobile: 931-242-1299
www.dynamicfiredesigns.com<http://dynamicfiredesigns.com>


Dynamic Fire Designs • 13063 County Line Rd., Box #87 • Spring Hill • FL • 34609

This message is confidential. It may also be privileged or otherwise protected by work product immunity or other legal rules. If you have received it by mistake, please let us know by e-mail reply and delete it from your system; you may not copy this message or disclose its contents to anyone. The integrity and security of this message cannot be guaranteed on the Internet.



________________________________
From: Sprinklerforum <[email protected]> on behalf of Ed Kramer <[email protected]>
Sent: Friday, June 15, 2018 9:20 AM
To: [email protected]
Subject: RE: Pump Discharge Piping


Does this pump supply any underground pipe, or 100% above-ground pipe?



Ed Kramer

Bamford Fire



From: Sprinklerforum [mailto:[email protected]] On Behalf Of Micah Davis, SET
Sent: Friday, June 15, 2018 8:50 AM
To: SprinklerForum <[email protected]>
Subject: Pump Discharge Piping



I have a fire pump installation that is having issues. The contractor has successfully completed a pump startup and test. During a separate follow up visit, the pump technician began having trouble getting the system back up to maintenance pressure after fire pump operation. The discharge piping has an elbow between the pump and the discharge check valve. It was first suggested that this check valve was defective, so it was replaced. The same problem was experienced after this replacement. It has been suggested that the elbow directly after the pump is causing turbulence that is preventing the check valve from closing properly. I can find nothing in NFPA 20 or the handbook to suggest this is a concern. Have any of you seen this? What would your recommendation be?



Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV


Dynamic Fire Designs





Mail: [email protected]<mailto:[email protected]>
Mobile: 931-242-1299
www.dynamicfiredesigns.com<http://dynamicfiredesigns.com>


Dynamic Fire Designs • 13063 County Line Rd., Box #87 • Spring Hill • FL • 34609

This message is confidential. It may also be privileged or otherwise protected by work product immunity or other legal rules. If you have received it by mistake, please let us know by e-mail reply and delete it from your system; you may not copy this message or disclose its contents to anyone. The integrity and security of this message cannot be guaranteed on the Internet.