James,

I believe the following sections would apply (2013 ed):

 

8.15.1.2.14  Vertical pipe chases under 10 ft2, where provided  in  multifloor  
buildings  where  the  chases  are  firestopped

at each floor using materials equivalent to the floor construction, and where 
such pipe chases shall contain no

sources of ignition, piping shall be water-filled or noncombustible and pipe 
penetrations at each floor shall be properly

sealed and shall not require sprinkler protection.

 

11.2.3.1.4  Restrictions. When either the density/area method or room design 
method is used, the following shall apply:

(4)  The following unsprinklered concealed spaces shall not require a minimum 
area of sprinkler operation of 3000 ft2

(h)  Vertical pipe chases under 10 ft2, provided that in multifloor buildings 
the chases are firestopped at each floor using 

materials equivalent to the floor construction, and where such pipe chases 
shall contain no sources of ignition, piping

shall be noncombustible, and pipe penetrations at each floor shall be properly 
sealed.

 

 

Thank you,

 

Bob Knight, CET III

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Litvak
Sent: Monday, June 25, 2018 11:09 AM
To: [email protected]
Subject: Combustible Concealed Void Spaces

 

**Sorry for the repeat send, first try had a typo in the subject** 

 

Often in wood construction there are void spaces caused by various situations, 
such as the shape of a bathroom around the bathtub, odd shaped dwelling units, 
etc. These spaces are inaccessible and have no insulation in them. Are 
sprinklers required in them, and why / why not? 

 

For context, we (me and coworkers) don't put sprinklers in those spaces because 
they don't have access. However, when questioned by an engineer, we are 
questioning the validity of using section 8.15.1.2.1 because we're not entirely 
sure if it's considered limited-combustible construction. Certainly the gypsum 
board on the studs is limited, but the wood studs themselves aren't. To help 
visualize, I've included a graphic. The areas in question are marked with 
asterisks. 

 

https://i.imgur.com/v1NIpYB.png

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to