It is a problem when the contractor is telling an owner that there is no 
problem because their calculation shows the system only requiring 40 psi when 
we know system pressures are going to actually be in the 200 psi range.

The issue is with designers who are not properly instructed on what the numbers 
mean in these calcs that they magically produce with a keystroke and with an 
owner who believes every word they say as absolute.

Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
[email protected] | www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Wednesday, June 27, 2018 2:42 PM
To: [email protected]
Subject: [EXTERNAL] Re: Real system pressures versus the calculations

This is not an issue that is intended to be caught by the hydraulic 
calculations for the system demand.  It is purely and simply a deficiency in 
the pump design (as already indicated by Matt).  The original design was fine 
but when someone changed the water supply, THEY  were responsible for ensuring 
the pump curve was still acceptable.

This is also a problem for new systems when water supply modifiers are applied. 
 You have to size the pump for both the sprinkler demand based on the lowest 
available supply pressure AND the churn limits based on the highest supply 
pressure.

Roland

Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.
Dallas, TX
http://www.firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.firesprinkler.org_&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=9t3lHhKjiD1mJlP5Tp1xAPihIkIokW1byvR67Hld0rY&s=EMtRTfazpYo9Jqx2Sw8CRcqLKHDKE_c9kkImir7w8dU&e=>

Fire Sprinklers Saves Lives




On Jun 27, 2018, at 8:21 AM, Prahl, Craig/GVL 
<[email protected]<mailto:[email protected]>> wrote:

I have a system that was originally designed with a fire pump taking suction 
from an elevated municipal water tank.  At some point in time the system source 
was changed from the tank to a municipal water supply.  This change has 
resulted in the system pressures being well over 200-250 psi.  So far nothing 
has blown out, yet but numerous buildings and underground were built based on 
standard pressure rated components.

The thought for the day is this, when you run a calculation, the output will 
show the minimum required pressure at the hydraulically most remote sprinkler 
that is required to provide the design flow rate.  The calculations also show 
the deviation between Required and Available system pressures.  So, when the 
fire pump kicks on, what the system ACTUALLY sees is the rated pressure of the 
pump being introduced into the system, not the minimum required pressure that 
is shown in the calculations, Agreed?

If it is stated that in the calculations that the pressure at the sprinklers on 
an upper floor will be less than 175 psi but those on the lower floor will be 
greater is it safe to assume based on the ACTUAL pressures coming out of the 
pump that the entire system will likely see pressures exceeding 175 psi?

Looking for some thoughts.

Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>

________________________________________________________________________________________
NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=6qYbbLx8x0UrMujmEGNoh-2hzoFD2d1EB5d2sQF0_OI&m=9t3lHhKjiD1mJlP5Tp1xAPihIkIokW1byvR67Hld0rY&s=LFqsvqTbG0TxwJkem9z0zSbj8aK8rryLlMulraGnZlA&e=>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to