NFPA 13(2016), 8.6.4 is for SSU and SSP.

Listed Residential Sprinklers have a very different requirement for the
pattern, so I would not use the same Position rules.

 

https://dps.mn.gov/divisions/sfm/programs-services/Documents/Quick%20Respons
e%20Newleter/QR0809SprayPatternsResidential.pdf

 

Brad

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jerry Van Kolken
Sent: Wednesday, July 18, 2018 1:45 PM
To: [email protected]
Subject: Vertical Change for Residential

 

Are there spacing rules like Figure 8.6.4.1.1.3 (A, B) for Residential
sprinkler? If this is still an regular 13 would that change the code?

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 