James,

I found there to be more issues with the storage of a Class II FCL then the 
storage of the wooden barrels.  At best it might be a Class III FCL (depends on 
the proof).  Dike sizes (containment) were a real problem on the proposed rack 
house here and ended up killing the project.  I was requiring sprinkler demand 
for Class II FCL stored x-feet high on some type of rack.  Never really got far 
enough for a density number.

Duane T. Fox, Jr., CFPS, CFI, CFPE
Asst Chief, Technical Services
DE State Fire Marshal's Office
302-856-5298



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Crawford
Sent: Monday, July 23, 2018 3:22 PM
To: [email protected]
Subject: Alchol in Wooden Barrels

We have a medium size distillery that will be storing the alcohol in wooden 
barrels to age, the barrels will be stored on multi-row racks to a height of 
30'.

We had suggested the Distilled Spirits standard and the AHJ does not want to 
accept it as a reference for the fire protection.

We have had a look in both NFPA #30 and FM data sheets  and can find nothing 
for the wooden barrels or the storage height.

Looking for other suggestions.


Thank you


James Crawford
Phaser Fire Protection Ltd.