Assuming you mean hose that is connected to a Class 2 standpipe or small hose 
connection supplied by a sprinkler system, I would reference NFPA 1962 (2018), 
ยง4.8.2.4:  Occupant-use hose shall be tested to the service test pressure 
marked on the hose.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield
Sent: Tuesday, August 07, 2018 4:15 AM
To: Sprinkler Forum
Subject: 5 Year Test Pressure for Fire Hose


Is the Test Pressure for 5 Year Maintenance on Fire Hoses 200 psi for 2 hours?



Mike