For remote FDC’s NFPA 24 (2013) Section 5.9.4.2 requires the automatic drip to 
be located in a location that permits inspection and testing as required by 
NFPA 25.

In industrial applications, ball drips not used on FDC’s are routinely used to 
drain daylighted FW piping that extends above grade for various applications.  
Good design will typically include a manual drain along side a ball drip since 
all ball drips I know of have a relatively low ‘seal pressure’.   Many 
applications exceed the this ‘seal pressure’ in head to the necessary 
configuration of the system.  Thus, the manual drain is required to drop the 
pressure below where the ball drip will then open.

It must be considered that any underground drain should be located inside a 
lined drain-field with ample volume so that any water being drained from the 
stack actually has somewhere to go and silt/mud does not plug the drain 
rendering it inoperable.  Water table elevation must also be considered.

Good luck,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer
O 952-656-3662 \  M 320-250-5404  \  F 952-229-2923
[email protected]  \  burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
*Registered in: LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: Sprinklerforum <[email protected]> On Behalf 
Of Dewayne Martinez
Sent: Thursday, September 20, 2018 9:11 AM
To: [email protected]
Cc: Dewayne Martinez <[email protected]>
Subject: buried fdc ball drip?

I have a contractor that is telling me that it is ok to run FDC piping trapped 
under ground and burying the drain 90 w/ ball drip at the bottom of the 
vertical pipe going up to the FDC above ground.  I was always taught that a pit 
was needed for the ball drip but I can’t verify it in NFPA 13 (13ed).
Can it be buried?
Thanks,

Dewayne Martinez
Fire Protection Design Manager

TOTAL Mechanical
Building Integrity

W234 N2830 Paul Rd.
Pewaukee, WI  53072
[email protected]<mailto:[email protected]>
Ph:  262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com/<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.total-2Dmechanical.com_&d=DwMFaQ&c=pgTKN5yjcEYSPUPpeP-zuA&r=NcyRL-K75Is7l5iUo7UtKsal2WbPG4sAR-BrZExi8dA&m=qblIJNsVUVbh_NH9UINW5irZtdHu2idUAjiwV0y_Mfk&s=5r55ANRX2TTtd8gWqs4ZtJwivi662CILk3VmGUe_y_w&e=>

[A close up of a sign  Description generated with high confidence]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to