Agreed.   Do not equate boat storage with this occupancy; the foam sandwich 
construction of most small boat hulls has exponentially more potential energy 
than the ATVs, even with the fuel.  Boat storage fires are … spectacular and 
devastating.    The car-stacker analogy works for me:  EH2.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Wednesday, October 24, 2018 1:34 PM
To: [email protected]
Subject: RE: Rack storage of ATVs

Boat storage presents a different challenge (versus cars) in that boats are 
open-topped containers. From what I understand they have a tendency to catch 
sprinkler water and then crush storage structures.

Matt


From: Sprinklerforum <[email protected]> On Behalf 
Of Nicky Marshall
Sent: Wednesday, October 24, 2018 3:16 PM
To: [email protected]
Subject: RE: Rack storage of ATVs

Yes, car storage sounds like a good suggestion, perhaps boat storage solutions 
also?

Nicky Marshall
Southern Regional Manager
PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Phone: +64 (0)3 579 5577 extn 1  Mobile: +64 (0)21 433 488  Email: 
[email protected]<mailto:[email protected]>  Skype: 
nicky-marshall Web :www.protechdesign.co.nz
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Postal: PO Box 4022, 
Redwood Village, Blenheim 7242, NZ

“I always wondered why somebody doesn't do something about that. Then I 
realised I was somebody” Lily Tomlin

From: Matt Grise <[email protected]<mailto:[email protected]>>
Sent: Thursday, 18 October 2018 7:43 AM
To: 
[email protected]<mailto:[email protected]>
Subject: RE: Rack storage of ATVs

Sounds similar to the automated car storage areas. Might look at one of those.

Matt


From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Fpdcdesign
Sent: Wednesday, October 17, 2018 1:41 PM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: Rack storage of ATVs

I was contacted by a company who is planning on storing ATVs WITH FUEL in racks 
to 12 ft. Each ATV will have 3-6 gallons of gas. Any thoughts on a commodity 
classification?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT