Can anyone tell me why this section is missing from the 2019 of NFPA 13? 25.2.1.4 Modifications to existing piping systems shall require testing at system working pressure. 25.2.1.4.1 Where modification is made to an existing system affecting more than 20 sprinklers, the new portion shall be isolated and tested at not less than 200 psi (13.8 bar) for 2 hours. 25.2.1.4.2 Modifications that cannot be isolated, such as relocated drops, shall require testing at system working pressure.
Best regards, *Joe Burtell, SET, CFPS* **PLEASE NOTE NEW PHONE NUMBER** [image: Burtell Fire_Small] Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>* 116 N. 11th Street | Billings, MT 59101 Email: j...@burtellfire.com Web Site: http://www.burtellfire.com *“**The bitterness of poor quality remains long after the sweetness of low price is forgotten.**”* *NOTICE:* The information contained in this e-mail transmission is intended only for use of the individual or entity named above. This e-mail transmission, and any documents, files, previous e-mail transmissions or other information attached to it, may contain confidential information that is legally privileged. If you are not the intended recipient of this e-mail transmission, or the employee or agent responsible for delivering it to the intended recipient, you are hereby notified that any disclosure, dissemination, distribution, copying or other use of this transmission or any of the information contained in or attached to this e-mail is strictly prohibited. If you have received this e-mail transmission in error, please immediately notify us by return e-mail transmission and destroy the original e-mail transmission as well as its attachments without reading or saving it in any manner. Thank you.
_______________________________________________ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org