Can anyone tell me why this section is missing from the 2019 of NFPA 13?

25.2.1.4 Modifications to existing piping systems shall require testing at
system working
pressure.
25.2.1.4.1 Where modification is made to an existing system affecting more
than 20 sprinklers,
the new portion shall be isolated and tested at not less than 200 psi (13.8
bar) for 2 hours.
25.2.1.4.2 Modifications that cannot be isolated, such as relocated drops,
shall require testing
at system working pressure.

Best regards,

*Joe Burtell, SET, CFPS*

 **PLEASE NOTE NEW PHONE NUMBER**

[image: Burtell Fire_Small]

Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*

116 N. 11th Street | Billings, MT 59101

Email: j...@burtellfire.com

Web Site: http://www.burtellfire.com

*“**The bitterness of poor quality remains long after the sweetness of low
price is forgotten.**”*

*NOTICE:*  The information contained in this e-mail transmission is
intended only for use of the individual or entity named above.  This e-mail
transmission, and any documents, files, previous e-mail transmissions or
other information attached to it, may contain confidential information that
is legally privileged.  If you are not the intended recipient of this
e-mail transmission, or the employee or agent responsible for delivering it
to the intended recipient, you are hereby notified that any disclosure,
dissemination, distribution, copying or other use of this transmission or
any of the information contained in or attached to this e-mail is strictly
prohibited.  If you have received this e-mail transmission in error, please
immediately notify us by return e-mail transmission and destroy the
original e-mail transmission as well as its attachments without reading or
saving it in any manner.  Thank you.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to