Is the interstitial space combustible?   If so, are  you proposing to sprinkler 
the space with sprinklers that satisfy the listing limitations of the CPVC?  
Does the CPVC also supply the OH space below?

[Steve Signature (3)]

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, December 12, 2018 9:29 PM
To: [email protected]
Subject: CPVC pipe passing thru ordinary interstitial space

I have a job that’s a 2 story building with an A truss roof, 1st floor is 
retail and 2nd floor is residential, the entire building is being sprinklered 
as per NFPA 13.

We want to install sidewalls with multiple CPVC risers and tie everything in 
1st floor interstitial space, Question is if there are any limitations of using 
CPVC pipe in the interstitial above an OHII occupancy.?

My initial taught is that since its protecting a light hazard occupancy it 
should be ok also the pipe is not exposed to the OHII (floor truss is being 
covered with 1 HR. rated assembly)

Does it matter that CPVC passes thru the ordinary space?