I HAVE A HOTEL THAT SAYS NFPA 13 DESIGN.
IF I USE RESIDENTAIL SPRINKLERS IN THE UPPER FLOORS. AM I CORRECT IN SAYING THAT I MUST USE .10 DESNITY EXAMPLE . I WAS GOING TO USE 18x18 4.9 K SPRINKLER REQUIRES 17 GPM @ 12 PSI FOR .05 DENSITY BUT SINCE NFPA #13 WOULD I BE REQUIRED TO DESIGN TO THESE NUMBERS. 32.4 GPM @ 43.72 PSI? OR AM I MISSING SOMETHING. THANKS