I HAVE A HOTEL THAT SAYS NFPA 13 DESIGN.

 

IF I USE RESIDENTAIL SPRINKLERS IN THE UPPER FLOORS. AM I CORRECT IN SAYING
THAT I MUST USE .10 DESNITY

 

EXAMPLE . I WAS GOING TO USE 18x18 4.9 K SPRINKLER

 

REQUIRES 17 GPM @ 12 PSI FOR .05 DENSITY

 

BUT SINCE NFPA #13 WOULD I BE REQUIRED TO DESIGN TO THESE NUMBERS.  32.4 GPM
@ 43.72 PSI?

 

OR AM I MISSING SOMETHING.

 

THANKS

 

 