I don’t know if you got any responses to this but I do not think it’s the 
intent to allow the use of residential sprinklers in corridors that serve any 
other occupancies but residential.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Friday, January 04, 2019 3:45 PM
To: [email protected]
Cc: Dewayne Martinez
Subject: Assisted living facility - residential sprinklers in corridors

NFPA 13 (13ed)
I am designing a multi-story assisted living facility where some of the floors 
have a dwelling units on the external perimeter connected by a common corridor. 
 Connected to the corridor is a group kitchen / eating / lounge and similar 
areas.  There is also a mixture of offices for the staff to use.  I was going 
to use residential sprinklers in the dwelling units, corridor and group areas 
and QR sprinklers in the offices and similar non-residential areas.  Sound 
alright?