We see this a lot out here because of a generally higher level of scrutiny by 
the AHJ community and also because of seismic loading.  Horizontal forces are 
trickier with any structure, but especially older buildings where the structure 
was designed to (sometimes much) earlier codes that didn't include adequate 
consideration for seismic reinforcement, if any.   We have two state agencies 
that perform separate plan reviews for fire/life safety and structural and that 
process requires that the SEOR and fire protection system designer co-own the 
details and basis of design for hangers and bracing.  We also get asked to do 
this occasionally on new construction in the private sector.    There are two 
ways to convey to the AHJ that the SEOR has reviewed and accepted anchorage and 
loads; one or both methods are pretty standard practice in CA when it's 
required:

1.  A letter, that need not be technical, stating that the SEOR has reviewed 
the fire sprinkler system design and finds that the structure will adequately 
support the pipe sizes and applied loads - both dead and shear - as proposed.

2.  The SEOR can include details of FP hangers, bracing and anchorage in their 
drawings.   We are doing this more and more; on the FP sheets we'll show a 
detail and then circle the anchorage with a tag that says, "See Detail 7/S-4.5" 
or similar.

3.  The SEOR adds her/his stamp to the FP details, with a letter that states, 
"Accepted per details on FP 4.5" or similar.


Steve L.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Irwin
Sent: Tuesday, January 08, 2019 3:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Structure certification

That makes sense,

Thanks Matt.

John Irwin
Quick Response Fire Protection



"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten." - Benjamin Franklin

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Matt Grise
Sent: Tuesday, January 8, 2019 6:08 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Structure certification

You might point them to the AHJ who wants the letter. I have done it both ways 
- get a letter rejected two or three times because the wording was wrong - and 
also calling them and asking exactly what it should say.

Matt


From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of John Irwin
Sent: Tuesday, January 08, 2019 5:05 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Structure certification

This isn't really my responsibility, but I have an AHJ looking for a letter 
from the structural engineer that certifies an existing building will hold the 
weight of the fire sprinkler system. The engineer on the project I am working 
on is asking for an example of what they letter should state. Does anyone 
happen to have an old letter or verbiage from a set of plans that I can take a 
look at? - Not my job, just trying to help a client out.

John Irwin
Branch Manager - West Coast
Quick Response Fire Protection
jir...@quickresponsefl.com<mailto:jir...@quickresponsefl.com>
CELL - 727-282-9243


"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten." - Benjamin Franklin


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to