Do a keyword search in NFPA 13. There is not a velocity limit imposed in NFPA 
13. It is basically self limiting. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Feb 28, 2019, at 6:32 AM, Rachid Saadaoui <[email protected]> wrote:
> 
> Hello
> I tried to make the calculations of a system deleuge for a
>   sulfur shed.
> In one section of the fire network piping supplying my deluge systems, the 
> speed is 9.2 m / s.
> I want to know the speed limit according to NFPA, either in my deluge system 
> and in the fire network that feeds the system.
> 
>  
>  
> PROTEC INCENDIE 
> Rachid SAADAOUI
> Ingénieur Chargé d'Affaire
> GSM : +2126 75 36 01 89
> TEL : +212522403232
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to