I had a similar situation in a Library children’s play area where there were 8 
or 10 disc/lighting features all at different heights and some overlapping and 
2m to 4m diameter. They were suspended below the ceiling 0.5 to 1.5m . All 
exceeded our Rules 1m maximum width for obstructions below sprinklers, so 
required sprinkler protection under and as they were not co-planar and close to 
each other could not fit the US research on “Cloud Ceilings”.

My understanding is the current US tests on clouds were based on eliminating 
sprinklers above the clouds when they were in close proximity to the solid 
ceiling above. Also the clouds were co-planar and in close proximity to each 
other.                                                 

In our case we installed sprinklers in each of the cloud discs and fully 
protected ceiling above.  For design purposes we operated two cloud sprinklers 
and the rest of the design number of  sprinklers on the ceiling above to make 
up the required design area/number.

 

Regards,

Russell Gregory

Christchurch New Zealand

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Tony Silva
Sent: Thursday, 7 March 2019 5:15 AM
To: [email protected]
Subject: Clouds

 

This is for a question I have been asked, and would like to get other opinions.

 

The building is a museum that has 5 to 6 feet diameter clouds simulating a tree 
canopy. There are so many of them at different elevations, that sprinklering 
below the clouds is not practical. Has anyone else come across this situation? 
If so, what has been the solution?

 

I was thinking, instead of providing sprinklers below the clouds, increasing 
the occupancy of the roof level sprinklers to OH2. Any other thoughts?

 

Tony