Yo, Greg!

As the Chair of the Standpipe Standard states..... call the FD and see what 
they say.

I live in a place much smaller than the Chair's locale.  We often defer to an 
automatic sprinkler system with a combined manual standpipe.  (It saves us on 
many jobs due to our lower volume city supplies.) Our FD folks usually take no 
exception.  However, if I were working in the norther parts (Chicago), they 
would not accept such an arrangement, no matter it's acceptability under the 
standards.  And I think this is with good reason...... density of people, 
complexity of staging, size of bldgs, etc.....


It should be recognized that the above is my opinion as a member of the NFPA 14 
Committee, and has not been processed as a formal interpretation in accordance 
with the NFPA Regulations Governing Committee Projects and should therefore not 
be considered, nor relied upon, as the official position of the the NFPA, nor 
any of their technical committees.

Sincerely,


Cecil Bilbo, prez and lead geek
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com<http://www.sprinkleracademy.com>
[email protected]<mailto:[email protected]>
??
OUR STUDENTS SAVE LIVES!!


________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Steve Leyton <[email protected]>
Sent: Thursday, March 7, 2019 7:18 PM
To: [email protected]
Subject: RE: GSA P100 Standpipes


Who is enforcing/interpreting the terms of your contract?  Assuming  you are 
conscribed to design and install per the referenced standards, then this 
creates a conflict in the terms and conditions of your contract that should be 
clarified by RFI.   As great as the pool of knowledge about all things 
water-based may be in the Forum, this is a contractual issue, not a code-based 
one.



If the responding fire department can furnish adequate flow and pressure (and 
that’s a performance standard they and only they can speak to) and a high 
maintenance link in the chain like a fire pump can be omitted, is that a bad 
thing?   There are two aspects to a water supply that are critical:  adequacy 
and reliability.    The reliability of a manual standpipe system goes to the 
source of water from which the FD takes suction.   If the building has pump, 
would it be arranged as a booster and take suction from that same source?  If 
so, then you face the same metrics for reliability either way.   But if the 
building would otherwise have a pump that takes suction from a tank that’s 
sized for both demand and duration, then reliability is enhanced and you have 
to weigh cost + maintenance + reliability to come up with the cost/benefit 
scenario, but you can argue that it’s a more reliable configuration, assuming 
that both pump and tank are meticulously maintained.



So I don’t have an answer because  you didn’t really pose a question, but if I 
was in your shoes and was being directed to undertake a design that didn’t 
conform to the code(s) and/or standard(s) that are referenced in my contract, 
I’d RFI whoever has jurisdiction over my contract and ask them (presumably the 
owner or their agent) for direction on how to proceed.



And please note well that EVERYTHING in this post is my personal opinion only.





Steve Leyton



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, March 07, 2019 5:05 PM
To: [email protected]
Subject: GSA P100 Standpipes



For those of you design professional that have been tasked with designing a 
standpipe for a GSA building, the Engineer for the govt is saying things that 
appear to be true but hard to accept.



It appears that there is not a requirement for an AUTOMATIC standpipe in a GSA 
building…..just the statement that “The building’s fire pump must be sized for

the sprinkler system requirements only if the

local responding fire department can provide

the necessary flow and pressure for manual

firefighting operations (i.e., standpipes),

through fire department connections.”



Therefore, regardless of height or floors, a manual standpipe can be used if 
the Fire Dept can provide enough water….no auto standpipe?



Thanks in advance,





Greg McGahan

Genesis Fire Services, LLC

4187 Farrington Road

Milton, FL 32583

o-850-637-8535

c- 850-712-9555


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to