Oops! Sorry! I was mistakenly looking at Table 16.2.1.3.3.1 when I references Curves A & B. In Table 16.2.1.3.3.2 both conditions use Curves C & D, but for encapsulated you increase the density by 1.5.
Larry Keeping From: Sprinklerforum <[email protected]> On Behalf Of Matthew J Willis Sent: March-21-19 9:58 AM To: [email protected] Subject: RE: Table Confusion How do we arrive at A and B in the Table? R/ Matt Matthew J. Willis, CWBSP Design Manager /3-D Specialist Rapid Fire Protection Inc.<http://rapidfireinc.com/> 1530 Samco Road Rapid City, SD 57702 Office-605.348.2342 Direct Line-605.593.5063 Cell-605.391.2733 Fax:-605.348.0108 [cid:[email protected]] From: Sprinklerforum <[email protected]<mailto:[email protected]>> On Behalf Of Larry Keeping Sent: Thursday, March 21, 2019 7:05 AM To: [email protected]<mailto:[email protected]> Subject: RE: Table Confusion You also must also look at other lines of Table 16.2.1.3.3.2. For nonencapsulated you need 1 level of in-rack sprinklers and you pick your density and design area based on Curves C or D. For encapsulated you need 1 level of in-rack sprinklers and you pick your density and design area based on Curves A or B and then you increase the density by a factor of 1.5. Best regards, Larry Keeping From: Sprinklerforum <[email protected]<mailto:[email protected]>> On Behalf Of Matthew J Willis Sent: March-20-19 7:06 PM To: [email protected]<mailto:[email protected]> Subject: Table Confusion NFPA 13 - 2016. Class IV Encapsulated- 18'-0" Table 16.2.1.3.3.2 tells me to go to Figure 16.2.1.3.2(d). The Figure description says "Class IV Nonencapsulated". But the table has "Yes" for encapsulated. Is this a typo, or is it just too late in the day? R/ Matt Matthew J. Willis, CWBSP Design Manager /3-D Specialist Rapid Fire Protection Inc.<http://rapidfireinc.com/> 1530 Samco Road Rapid City, SD 57702 Office-605.348.2342 Direct Line-605.593.5063 Cell-605.391.2733 Fax:-605.348.0108 [cid:[email protected]]
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org