Hi Tim,
Substitute the word “Dry” for open or manual. The intent is to always use 
galvanized pipe in systems where water isn’t continuously present in the piping 
system.  Open Spray Deluge Systems and Closed Head Manual Systems present these 
conditions. They are “Special Hazard “ fire protection systems commonly 
utilized in the petro-chemical, power generation, and vegetable oil extraction 
industry.
Scot, chime in here and elaborate on the topic.

Mark at Aero
602 820-7890

Sent from my iPhone

On Mar 28, 2019, at 4:45 AM, Easter, Tim (Contractor) 
<[email protected]<mailto:[email protected]>> wrote:

NFPA 15 §5.3.6.1 steel pipe used in manual and open systems shall be galvanized 
on its internal and external surfaces IAW Table 5.3.1.

What is an open system? Deluge?

What is a manual system? Fusible link or glass-bulb?

These systems are not defined in NFPA 15 or 13. Is there an automatic system?
Or other types of systems?

The verbiage is confusing, any help is appreciated.

Best,
Timothy M. Easter, P.E.
Fire Protection Engineer
BAE Systems, Inc.
T: +1 423 578 1713  |  E: 
[email protected]<mailto:[email protected]>

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=6ltOtE2A8edUMp9X1nv4A16L8cIA-UoKAq0_BZ3Nhn8&s=xAjPtY1tyn2Ux4g6ujzDorFneB8gvrq5VsdkqI4ioaw&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to