My interpretation is that if the top of the suspended or floor-mounted 
obstruction is more than 18" below the deflector, then you can ignore it for 
obstruction purposes in regardless of if it is light or ordinary hazard. If 
ordinary hazard, the obstruction MUST be at least 18" below the deflector. If 
light hazard, then you are allowed to use the table to determine if your 
sprinkler is obstructed.

Since your ceiling is exactly 18" above the partition walls, it looks like  
you're hosed (since the deflector will be at least some distance lower than the 
ceiling). But if you could get the owner to make the units, like, 8'-4" tall, 
then maybe you would be good to go. At least, that is, if your ceiling is open 
enough to not be a obstruction.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Nick Maneen
Sent: Monday, April 22, 2019 1:39 PM
To: [email protected]
Subject: [EXTERNAL] Floor mounted obstructions EC OH

Good afternoon all,
I have an existing open office with 10'-0" ceilings protected by EC LH (18x18) 
pendent sprinklers.  The new owner of the building would like to put in 8'-6" 
tall self-storage units with open mesh ceilings.  They have fantastic water and 
I would like to switch the sprinklers to ECOH and recalculate to prove the 
system works.  The issue is that 8.8.5.2.2 in the 2013 and 2016 editions of 
NFPA 13 (11.2.5.2.2 in the 2019 Edition) only references light hazard 
occupancies.
Okay, 8.8.5.2.2 doesn't apply for 18" of clearance.  What does apply?  What if 
I was 36" above the partition?  More?
It looks like I need to protect each unit individually and use baffles when the 
sprinklers get too close.  What do you think?

[Description: cid:[email protected]]

Nicholas Maneen, SET / Estimator-Project Manager
2553 South Fayetteville Street
Asheboro, NC 27205
p 336.625.2304
f  336.625.4649
c 704.791.7789
www.Sentryfp.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.sentryfp.com_&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=j6DbeqdCisQ3RT8tQv8ea7tAj3yJs1ysQi_4TL1JRN8&s=ZxV6YEKodxXjxAG0qa9AqwLGmLn3vkCP5I_AMEqHxOQ&e=>

       [Description: QualityContractor-Logo]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to