Matt,

Has the project been as far as a pre-application mtg? If so this likely has 
already been discussed. Ring the fire plan reviewer. Their pre-app letter might 
be a place to start discussion.

Best.

Bruce Verhei 

> On May 2, 2019, at 14:13, Nick Maneen <[email protected]> wrote:
> 
> From what you describe and depending on how the IBC is modified in your area, 
> typically the upper levels wouldn’t require sprinklers.  However, I am with 
> you that because the lower 2 levels do require sprinklers, the entire 
> building requires sprinklers.  There may be a local P.E. that would disagree 
> and say otherwise, but I would have that in writing and blessed by the local 
> AHJ.
>  
> Nick Maneen, SET 
> c 704.791.7789
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Matt Grise
> Sent: Thursday, May 02, 2019 4:44 PM
> To: [email protected]
> Subject: partially enclosed parking
>  
> I am looking at a 5-level parking garage that will have 2 levels below grade. 
> The 2 below grade levels will be enclosed – so they will need sprinklers, but 
> the top 3 levels will be open. I can’t recall – do the open levels need 
> sprinklers? I know NFPA does not normally allow a partially protected 
> building, but for some reason I was feeling like it might be ok to omit 
> sprinklers from the above grade levels.
>  
> Thanks!
>  
> Matt
>  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to