This one is for anyone with marine experience. Ref: NFPA 13 (2013) 26.4.12.6. This is under the sub heading of Alarm Signals and Devices. “Sprinkler zones shall not encompass more than two adjacent decks or encompass more than one main vertical zone.”
The AHJ is saying that the sprinkler systems have to be separated in this manner. My thought is that this only deals with the alarm zones and not the sprinkler system. I have seen this similar situation on the commercial side where there were multiple alarm fire zones on one floor with only one sprinkler system zone. Any feedback is welcome. Dale F. Wingard, SET Designer Commercial/Marine Division NICET IV #76284 Water-based Systems Hiller Systems A Division of The Hiller Companies, Inc. 3751 Joy Springs Drive Mobile, AL 36693 o: 251.661.1275 ext. 10145 HillerFire.com [Macintosh HD:Users:andrechiang:Dropbox:Emily's Files:Hiller:Email Signature:Hiller100 Email Signatures 2019-01-10:Hiller100 Email Signatures V1 2019-01-10 - Systems.png] Protecting life and property since 1919