Vince, Nioce answer to dumb question
*Glen Bue**low* *Glen W. Buelow, Inc.* *Fire Protection Design and ConsultingCleveland 330.220.7201 <330.220.7201> *●* Akron 330.665.4439 <330.665.4439>* On Wed, May 15, 2019 at 2:26 PM Vince Sabolik <[email protected]> wrote: > Height x .434 = Starting psi at top. > > Less friction loss at flow (pick a flow) > > Your flow test complete with a K factor! > > > > > > > On 5/15/2019 11:27 AM, Mike Stossel wrote: > > I have an existing building with a sprinkler system that is supplied by a > gravity tank located on the roof. They are modifying the first floor of > the building that will require hydraulic calculations. Is it possible to > mathematically create a waterflow test accurately, or do you need to > actually perform a water flow test at the 1st floor level? > > > > Mike Stossel *SET* > > [image: 400dpiLogoCropped] > > 36 Barren Road > > East Stroudsburg, PA 18302 > > Office: 973-670-2627 > > [email protected] > > > > _______________________________________________ > Sprinklerforum mailing > [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > > -- > > 11351 Pearl Road / Suite 101 > Strongsville, Ohio 44136 > Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601 > > > * Vince Sabolik * > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >