> Height x .434 = Starting psi at top.
>
> Less friction loss at flow (pick a flow)
>
> Your flow test complete with a K factor!
>
>
>
>
>
>
> On 5/15/2019 11:27 AM, Mike Stossel wrote:
>
> I have an existing building with a sprinkler system that is supplied by a
> gravity tank located on the roof.  They are modifying the first floor of
> the building that will require hydraulic calculations.  Is it possible to
> mathematically create a waterflow test  accurately, or do you need to
> actually perform a water flow test at the 1st floor level?
>
>
>