As I understand it, the Table is based on test data using ½ and large orifice 
sprinklers, which don’t always give the best results against high piled 
storage, so that could explain some of the inconsistencies.

Having said that though, it looks to me that Column C is generally less 
demanding than Column E.
ie. For 20 ft storage in a 25 ft high building, Col. C wants a 0.60 density 
whereas Col. E wants 0.70.

Best regards,

Larry Keeping

From: Sprinklerforum <[email protected]> On Behalf 
Of Dewayne Martinez
Sent: May-20-19 2:50 PM
To: [email protected]
Cc: Dewayne Martinez <[email protected]>
Subject: NFPA 13 (2013ed) figure 15.2.2

Group A plastics, 5-12ft of storage, 15 to 20ft ceiling
Figure 15.2.2 / table 15.2.6(a)

Why is Group A, Expanded, Cartoned, Stable (Column E) less of a hazard then 
Group A, nonexpanded, stable, cartoned  (Column C)?
One would think that since the expanded has a higher heat release rate so it 
would be higher density.  Can anyone help me understand this?

Thanks,
Dewayne Martinez