I saw a couple of discussion chains about nail plates from 2009, but I thought 
I would check back in with the forum to see if there have been any new 
developments.

I recently came across a building inspector who says that the 3"x 5" nail 
plates we have been using do not meet code. The explanation that I received was 
essentially "since NFPA and IFC do not dictate the size of the nail plate - or 
even call out nail plates at all - , the IPC plumbing code is the automatic 
default (since both are dealing with plastic pipe CPVC/PVC), and therefore the 
guidelines of the IPC apply to CPVC fire sprinkler installations."

I can't find that "code requirement" in any published documentation, and the 
code official did not indicate that such a fallback requirement was published 
anywhere.

My position is that nail plates are a 'best practice' and the sizes are not 
dictated by the code for fire sprinkler systems. If they would like to use IPC 
as a guide, that is fine... but since they have only brought this up halfway 
through a job, why don't we leave the 3x5 plates installed since they don't 
actually violate the code.

Their position is that the 3x5 plates are in violation of the building code 
since they don't meet the plumbing code and should be removed and replaced with 
4" tall plates in accordance with IPC 305.6.

Has anyone come across any documents or discussion on this topic recently? I 
have an informal interpretation request pending with ICC, but I don't get that 
back for four more days.

Thanks!

Matt