FM has design criteria for this scenario, see data sheet 8-9 Table #9 you
start with the roof height so if you need 30' of storage then most likely
you have as a minimum a 35' roof height. This table shows K25 ESFR 12@60
that is in fact your only option in this table. Its interesting that per
NFPA 13 2016 edition 17.3.3.5 protection of exposed expanded plastics is the
same k25 ESFR and at the same design pressure.

Good luck

 

From: Brian Harris <[email protected]> 
Sent: Tuesday, June 25, 2019 5:04 AM
To: [email protected]
Subject: ESFR Heads & Cartoned Expanded Plastics 

 

Does anybody know of an ESFR head that will work for cartooned expanded
plastics up to 30' storage? All my searches only allow up to 25' storage.

 

Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com <http://bvssystemsinc.com/> 

Phone: 704.896.9989

Fax: 704.896.1935

 