I don’t recommend to leave exhaust near people that can be affected by CO gases. As this is an emergency equipment we cant treat it as a car running, but also also this is not a car, this is like truck running. Also NFPA 20 states:
In the other extreme, there are codes with too much restrictions. For example the code in my country (Perú), require exhaust to be delivered to the roof of the building, so in some cases it is hundreds of feet. To do so, we have to use the software of the motor supplier to find the appropriate diameter for the exhaust. I think there is no restriction on length of the exhaust if you respect the diameter from the calculation of “Exhaust Backpressure”. As most of the motors at present time are made by Clarke, you can follow their online software to do so. <http://www.clarkefire.com/design-tools/pump-room-calculators/exhaust-backpressure-calculator> http://www.clarkefire.com/design-tools/pump-room-calculators/exhaust-backpressure-calculator Saludos Cordiales Jussef Liban Gerente Sigueme en las redes para obtener información sobre temas relacionados con la protección contra incendios. GRUPO TELEGRAM: <https://t.me/joinchat/JmalzBDcEYE8NDqSwbfrBg> https://t.me/joinchat/JmalzBDcEYE8NDqSwbfrBg FACEBOOK: <https://www.facebook.com/seguridadcontraincendiosalalcancedetodos/> https://www.facebook.com/seguridadcontraincendiosalalcancedetodos/ FACEBOOK: <https://www.facebook.com/grupo3speru/> https://www.facebook.com/grupo3speru/ ARTICULOS TECNICOS COLECCIONABLES: <https://grupo3s.pe/biblioteca/> https://grupo3s.pe/biblioteca/ LINKEDIN: <https://www.linkedin.com/in/jussef-liban-114b56b9/> https://www.linkedin.com/in/jussef-liban-114b56b9/ YOUTUBE: <https://www.youtube.com/user/JussefLiban/featured?view_as=subscriber> https://www.youtube.com/user/JussefLiban/featured?view_as=subscriber De: Sprinklerforum <[email protected]> En nombre de Phong - Indochine Engineering Enviado el: miércoles, 31 de julio de 2019 20:02 Para: [email protected] Asunto: RE: Engine Exhaust of a Diesel fire pump Thanks Craig, Understand that the diesel exhaust of the fire pump is similar to a diesel car in parking area? Regards, Le Vu Phong Mobile: +84 (0) 902 363 525 From: Sprinklerforum <[email protected] <mailto:[email protected]> > On Behalf Of Prahl, Craig/GVL Sent: Wednesday, July 31, 2019 6:50 PM To: [email protected] <mailto:[email protected]> Subject: RE: Engine Exhaust of a Diesel fire pump Typically we would not choose a diesel pump if our pump room were in a basement or any room where we could not get the exhaust out of the room with the shortest possible length of pipe. Discharging exhaust into a parking basement would need to be approved by a building code official since this could pose a hazard to people who might be in the parking area if the pump were running. You also need to speak to the pump manufacturer about the length of the exhaust because excess length affects pump performance. The ventilation system may not be suitable for moving diesel exhaust. Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | <mailto:[email protected]> [email protected] | <http://www.jacobs.com/> www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 From: Sprinklerforum <[email protected] <mailto:[email protected]> > On Behalf Of Phong - Indochine Engineering Sent: Wednesday, July 31, 2019 4:21 AM To: [email protected] <mailto:[email protected]> Subject: [EXTERNAL] Engine Exhaust of a Diesel fire pump Dear All, I have this fire pump installed inside a pump room in a basement of a high rise tower. The space of basement outside the pump room is for parking. Read 11.5 of NFPA 20:2019 and I design to select the exhaust discharge location just outside the pump room, and inside the parking basement. The basement have its dedicated auto operated ventilation system. Is my design not wrong to NFPA? Thanks. Regards, Le Vu Phong Mobile: +84 (0) 902 363 525 _____ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org