I think this is one of those things, just like with Hi-Ex foam generators, 
where you really want to get some input from the manufacturer.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Prahl, Craig/GVL
Sent: Thursday, August 8, 2019 8:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: 30' diameter and 30' high storage tank

Spray nozzles are selected based on their angle of spray.  So depending on the 
distance off the wall of the tank, the pressure and flow characteristics, you 
select your nozzle.  Once you know what the area of coverage based on the above 
info will be for the nozzle, you can determine the horizontal spacing since 
there needs to be some overlap of the spray pattern in order to insure complete 
coverage of the tank surface.  You do not want a ton of over spray nor do you 
want dry spots.  There is no specific spacing rules as there are too many 
variables for anyone to make a blanket statement on spacing.

As far as vertical, 12 ft. is subjective also.  If there are appendages off the 
tank which could interrupt run-down or deflect the spray pattern, you might 
need to have them closer.  In the vertical the spray impingement may not 
contact the tank wall 100% between nozzles but you have run-down that is taken 
into consideration to some extent.

Check your email  inbox.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.jacobs.com_&d=DwMFAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=UlKWpTB5Cum9vJEFVDR00XnSSTmzOu0NITkY_43dMH4&s=P3PlyEfsimUF_KTKonkk8ZU6dRBpmWnfePtdqVVq3xY&e=>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Easter, Tim (Contractor)
Sent: Thursday, August 8, 2019 11:34 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [EXTERNAL] 30' diameter and 30' high storage tank

How do you space nozzles horizontally on a 30' diameter flammable liquid 
storage tank? I know to space 12' vertically. My question is horizontally.

Best,
Timothy M. Easter


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to