As with everything in our business, the Building and Fire codes govern when and 
where what type of fire alarm system is or is not required.  That's the 
starting point.  NFPA 72 gives the direction on installation details and other 
requirements for the systems.  Some facilities require everything, pull 
stations, horn/strobes, evacuation, etc.  Other conditions might require no FA 
system at all and there's different situation with requirements in between both 
extremes.

Sometimes, owners or their insurers desire to have a FA system installed even 
when it's not required by Code.  That's their option.  But if they opt to have 
one, the design and installation still has to follow NFPA 72.  They can't just 
create some cobbled together "system".

Typically the FA requirements are based on the occupancy of the building which 
is typically defined by the Architect of record.  But if there isn't one (an 
architect), it's not that difficult to determine what the occupancy will be as 
defined by the IBC.

There are other factors involved in determining what type of FA system is 
required such as whether or not you have sprinklers.  There are also what is 
called Special Function systems where you have an alarm panel supervising 
sprinkler systems but you have no other typical FA devices like pull stations 
or strobes.

This is the super simplified explanation.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum <[email protected]> On Behalf 
Of John Irwin via Sprinklerforum
Sent: Tuesday, August 13, 2019 5:32 AM
To: [email protected]
Cc: John Irwin <[email protected]>
Subject: [EXTERNAL] Fire Alarms

I would guess some of you are pretty familiar with fire alarm code as well as 
sprinkler code. Our fire alarm division falls under my purview and I really 
don't know the first thing about them. They certainly don't seem to follow the 
same reasoning we use when determining how we are going to protect a building 
with sprinklers. The client base isn't the same, the way they bid and sell them 
isn't the same. They seem to have less regard for what's actually required and 
more interest in what the bid plans show.

Are they like sprinklers insofar as ... this book says fire alarm yes or no ... 
this book tells you what's required ... this book tells you how to design 
them... etc ?

Can anyone recommend where or how I can get some basic knowledge of how alarms 
should be done? Probably starting with 101, 72 and ... 70? Design class or code 
class? Does anyone have a fire alarm design class like AFSA and NFSA do for 
sprinklers?



John Irwin


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to