Is there any way to drop the unit heaters down so that they are at least 7 feet 
below the deflectors, thus solving the temperature and obstruction issues?

You bring up a good point, but a unit heater a foot away at that elevation is 
going to create one helluva obstruction for the ESFR sprinkler. I would argue a 
much worse obstruction than some of the examples that are clearly not allowed. 
But I'm interested to hear some more feedback.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ed Kramer via Sprinklerforum
Sent: Tuesday, August 20, 2019 8:21 AM
To: [email protected]
Cc: Ed Kramer <[email protected]>
Subject: RE: [EXTERNAL] ESFR's and unit heaters

The temperature rating is a whole separate issue.  Due to the structural layout 
of this existing building, the ESFR's are  not on a 10' x 10' spacing. So 
literally impossible to get heaters 7' away.  Still working on that one.  May 
have to go to another source of heat.

Back to the 'obstruction at or near ceiling'.  Without 13 giving any other 
clarification, I interpret 8.12.5.2 to apply to any isolated obstruction that 
is entirely below the elevation of the sprinkler - even if it's only 1/2".  I 
believe 8.12.5.1 is titled "Obstructions at or near ceilings" because it 
applies to objects who's tops  are located in the space between the ceiling and 
the sprinkler deflector.  Any objects that are located entirely below the 
deflector kicks you to 8.12.5.2 or 8.12.5.3.  I'll admit, I don't work with 
ESFR's every day, but having read those sections multiple times, that's all I 
come up with.

Ed K

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery via Sprinklerforum
Sent: Tuesday, August 20, 2019 9:48 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Kyle.Montgomery 
<[email protected]<mailto:[email protected]>>; Ed Kramer 
<[email protected]<mailto:[email protected]>>
Subject: RE: [EXTERNAL] ESFR's and unit heaters

Also, how are you complying with the temperature rating when you are that close 
to a unit heater? Are they making any high temperature ESFRs yet?

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Kyle.Montgomery via Sprinklerforum
Sent: Tuesday, August 20, 2019 7:40 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Kyle.Montgomery 
<[email protected]<mailto:[email protected]>>; Ed Kramer 
<[email protected]<mailto:[email protected]>>
Subject: RE: [EXTERNAL] ESFR's and unit heaters

I'm looking at the code again, and you may be right. But I always thought that 
an obstruction that close to the sprinkler (could you quantify "just below the 
ESFR deflectors") would have to meet the rules for "Obstruction at or Near 
Ceiling", 8.12.5.1.

Are we saying that 8.12.5.1 only applies if the obstruction extends above the 
deflector? I thought that anything in that 0"-31" below the deflector range 
(shown in Table 8.12.5.1.1) was considered "at or near the ceiling".

Kyle Montgomery
 [cid:[email protected]]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ed Kramer via Sprinklerforum
Sent: Tuesday, August 20, 2019 6:23 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Ed Kramer <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] ESFR's and unit heaters

I'm looking for a bit of a reality check this morning.   Got an ESFR sprinkler 
system and unit heaters.  In plan view, the heaters are 21" by 40".  Top of the 
heaters will be just below the ESFR deflectors, and they will be located at 
least 1' horizontally from the ESFR sprinklers.  It appears that NFPA 13 (2013) 
section 8.12.5.2 applies.

Subsection (2) reads: "Additional sprinklers shall not be required where the 
obstruction is 2 ft or less in width and the sprinkler is located horizontally 
1 ft or greater from the nearest edge of the obstruction."

Since the heater is 2' or less in its smaller dimension (width), does it matter 
that the other dimension (length) is greater than 2'?  I say the length is not 
relevant (unless its long enough to obstruct more than 1 sprinkler, then 
section 8.12.5.3 applies), and subsection (2) allows me to not install a 
sprinkler below these heaters.

How do the rest of you interpret this?

Thanks
Ed Kramer
Bamford Fire