Use the standard that applies to a transition boundary between two different 
application densities. You are transitioning between the application above the 
mechanical platform to the zero application above the remaining ceiling cavity 
space. 

> On Sep 6, 2019, at 1:05 PM, Bobby via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
> I have an office building with ceiling throughout, non combustible 
> construction. There is a closet that has no ceiling, walls don't go to deck, 
> and it has a ships ladder that leads to a 20x20 mechanical platform above the 
> ceiling, also of non combustible construction. This platform has 3'-0 knee 
> walls around it. 
> 
> How far past this platform is required to be sprinklered. Because of the open 
> ceiling stairs closet, does 8.15.23.3. truly apply - if not what does?
> 
> Thank you,
>  
> Bobby Gillett
> Seago Fire Protection
> 850-217-3899 Pensacola Area Office
> 
> 850-836-2288 Main Office  
> 850-836-2277 fax
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org 
> <mailto:Sprinklerforum@lists.firesprinkler.org>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>