Thanks guys. I knew it was in there, just had a brain freeze and could not
remember where to find it.

Bruce Hermanson

President

 TSFP

47810 Galleon Drive

Plymouth, MI 48170

(734) 454-1350

 

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Tuesday, October 08, 2019 12:31 PM
To: [email protected]
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G; 'Ron Greenman'
Subject: RE: Upright Sprinkler

 

That is for CMSA only.  Using standard spray, you want to look at
8.6.5.2.1.8.  That is the reference for smaller than 3" not needing to meet
the 3x rule.  For 3" and larger, you must comply with 3x rule for standard
spray.

 

 <http://www.mfpdesign.com/> MFP_logo_F

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

 <mailto:[email protected]> [email protected]

www.mfpdesign.com

 

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

 

From: Sprinklerforum <[email protected]> On
Behalf Of Ron Greenman via Sprinklerforum
Sent: Tuesday, October 8, 2019 9:27 AM
To: [email protected]
Cc: Ron Greenman <[email protected]>
Subject: Re: Upright Sprinkler

 

>From the 2016 Handbook

 

8.11.5.2.2 Branch Lines. Upright sprinklers shall be positioned with respect
to branch lines 
in accordance with one of the following:
(1) Upright sprinklers shall be permitted to be attached directly to branch
lines less than or 
equal to 4 in. (100 mm) nominal in diameter.
(2) Upright sprinklers shall be permitted to be offset horizontally a
minimum of 12  in. 
(300 mm) from the pipe.
(3) Upright sprinklers shall be permitted to be supplied by a riser nipple
(sprig) to elevate the 
sprinkler deflector a minimum of 12 in. (300 mm) from the centerline of any
pipe over 
4 in. (100 mm) nominal in diameter.
Research conducted by FM Global has demonstrated that sprinklers will
operate properly as long as the 
sprinkler is located within the required vertical distance between it and
the ceiling above. In addition, 
testing has demonstrated that there is not a sizable reduction in actual
delivered density when upright 
sprinklers are installed in the presence of a 4 in. (100 mm) wide object
located directly below them. Sprigs 
or riser nipples are not necessary for upright sprinklers as long as the
diameter of the pipe does not exceed 
4 in. (100 mm).
When an upright sprinkler is installed directly on the branch line, the
branch line becomes an obstruction.
As the branch line pipe size is increased, the "pipe shadow," or area below
the sprinkler that is affected, 
increases. Because CMSA sprinklers attack the fire, this obstruction can
have a significant impact if the fire is 
located directly below the sprinkler and is a concern when the branch line
piping is larger than 2 in. (50 mm).
Many systems require larger piping to meet the hydraulic design requirements
of the CMSA sprinkler. 
Raising the sprinkler on a riser nipple reduces the angle of obstruction by
limiting the area affected by the 
obstruction to no more than would be created by a smaller branch line.
Another approach to the problem is taken in 8.11.5.2.2(2). If the sprinkler
is offset at least 12 in. (300 mm), 
the discharge from the sprinkler can flow under the branch line. This
position eliminates the obstruction or 
limits the impact of the obstruction caused by the branch line so that it
does not pose a significant problem.


 

 

Ron Greenman


[email protected]

253.576.9700

 

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera director
(1942-)

 

 

On Tue, Oct 8, 2019 at 9:17 AM Bruce Hermanson via Sprinklerforum
<[email protected]> wrote:

Did NFPA remove the requirement where upright sprinklers attached to pipe 3"
or larger needs to be on a sprig?

I remember seeing it in past editions but cannot find it in 2016.

 

Bruce Hermanson

President

 

TSFP

47810 Galleon Drive

Plymouth, MI 48170

(734) 454-1350

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to