There is a simple way to deal with the problem: Include the cost of the flow 
test in your pricing. The costs gets passed on to your client. 

Sure, it’s a pointless cost. But, many jurisdictions have pointless costs that 
just go along with the costs of doing business. 

I agree it would be beneficial to get the cost removed because it does not 
provide any added benefit. However, is this a hill you are willing to die on? 
If not, just pass the cost on to the client and move on. 

Have a happy Thanksgiving. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
www.mfpdesign,com
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Nov 27, 2019, at 3:50 PM, Owen Evans via Sprinklerforum 
> <[email protected]> wrote:
> 
> 
> Review: The water purveyor, after 19 years of providing static pressure only 
> for the development of 13D calculations, is now requiring a fire flow test 
> for 13D systems at a cost of $600.00.
> 
> I emailed and asked the operations manager for the water purveyor to provide 
> me the justification for the change. He emailed back and said: "Our internal 
> engineering management team and the City's building department determined 
> that static pressure only was inadequate for official fire sprinkler 
> calculation purpose". (mouth hanging open) I contacted the fire, building, 
> engineering, and planning departments, they all denied agreeing to such a 
> change.
> 
> I emailed the Division Chief for the fire prevention bureau (who is brand 
> spanking new in his position) about this issue. He emailed back and said; 
> "NFPA 13D section 10.1.2 allows for static pressure only when from a 4" or 
> larger main. NFPA does not mandate this method nor does it exclude the more 
> restrictive and costly flow testing".  YES! He said that!  The Division Chief 
> is out of the office until Monday. I hope to speak with him then. 
> 
> In the meantime I'm dumbfounded wondering how to deal with this problem. I 
> feel like I'm dealing with Harry and Lloyd. 
> 
> Well, I thought you all would find this entertaining. Happy Thanksgiving and 
> safe travels to all.
> 
> Owen Evans
> 
> 
> 
> 
> -----Original Message-----
> From: firstin--- via Sprinklerforum <[email protected]>
> To: sprinklerforum <[email protected]>
> Cc: firstin <[email protected]>; Bruce Verhei <[email protected]>
> Sent: Tue, Nov 19, 2019 2:38 pm
> Subject: Re: [EXTERNAL] Not required, requirement
> 
> Ha! I was wondering. 
> 
> Sent from my iPhone
> 
> > On Nov 19, 2019, at 2:23 PM, Bruce Verhei via Sprinklerforum 
> > <[email protected]> wrote:
> > 
> > When I say I don’t get it, I mean I don’t get why someone wants a full 
> > flow test for a two head system.
> > 
> > 
> > 
> >> On Nov 19, 2019, at 08:01, Steve Leyton via Sprinklerforum 
> >> <[email protected]> wrote:
> >> 
> >> Owen:
> >> 
> >> How long did you work as a fire official?  More than a couple years if I'm 
> >> not mistaken, so I assume in that time you had correspondence with one or 
> >> more water purveyors, correct?    There are several factors here that do 
> >> not serve the community but DO serve the water company.  The cost to the 
> >> customer is onerous and simply adds to the cost of the fire sprinkler 
> >> system, which is 180° contrary to the State Fire Marshal's mission that 
> >> the costs of residential sprinkler systems be closely managed at every 
> >> turn.  The information generated is superfluous as we don't need the 
> >> residual at a high fire flow.  For their sake, they generate a certain 
> >> amount of revenue and get to exercise one or more hydrants so they're 
> >> essentially covering the costs of what used to be overhead (assuming they 
> >> actually exercised the hydrants on their system historically).  
> >> 
> >> So you can do two things:  1) Roll up your sleeves and be part of the 
> >> solution or, 2)  Wave your hands wildly and complain in a loud voice about 
> >> the injustice of it all.  Having exercised #2 already, I implore you to 
> >> try #1.    First, verify with the serving fire department that Static - 
> >> 10% is acceptable to them for SFD submittals.  Then, craft a flow test 
> >> curve and show the two points provided by the water purveyor and add a 
> >> point where the flow rate of the residential sprinkler system falls right 
> >> next to the static on that curve.  Write a cover letter addressed to the 
> >> director of engineering for the water purveyor explaining how Static - 10% 
> >> will provide an accurate basis for these systems and that such a practice 
> >> is acceptable to the serving fire department(s) and asking them to change 
> >> their policy.    Emphasize that the added cost goes against best practices 
> >> and intentions and is contrary to the overarching mission of raising the 
> >> level of fire/life safety in the residential built environment.  Then send 
> >> it to the DOE with CC copies to the Director (if public) or the 
> >> President/CEO/COO (if private) or General Manager of the water purveyor.  
> >> Also copy the serving fire marshals.
> >> 
> >> Be part of the solution.
> >> 
> >> Steve Leyton
> >> 
> >> -----Original Message-----
> >> From: Sprinklerforum 
> >> [mailto:[email protected]] On Behalf Of 
> >> firstin--- via Sprinklerforum
> >> Sent: Tuesday, November 19, 2019 4:45 AM
> >> To: [email protected]
> >> Cc: [email protected]; Bruce Verhei
> >> Subject: Re: [EXTERNAL] Not required, requirement
> >> 
> >> Bruce,
> >> 13D allows calculations to be developed from static pressure only when the 
> >> system is being supplied from a reliable water supply like a municipal 
> >> system. Because the demand of a 13D system is so minimal (26 gpm, two 
> >> heads flowing) a water supply curve developed from a flow test (static, 
> >> residual, and flow) is not required. The water company charges $600 to 
> >> perform a flow test. Our forefathers developed the 13D standard to be a 
> >> minimal system to keep the cost down to reduce the resistance from 
> >> developers and municipalities. A flow test for a 13D system is monumental 
> >> waist of time and money. But try and explain that to the new inspector 
> >> (who has all the power yet very little knowledge and training) who is just 
> >> passing through on the promotional track. Very frustrating. 
> >> 
> >> Sent from my iPhone
> >> 
> >>>> On Nov 18, 2019, at 11:28 PM, Bruce Verhei via Sprinklerforum 
> >>>> <[email protected]> wrote:
> >>> 
> >>> I don’t get it. It’s not off a home well.
> >>> 
> >>> 
> >>> 
> >>>> On Nov 18, 2019, at 20:24, firstin--- via Sprinklerforum 
> >>>> <[email protected]> wrote:
> >>>> 
> >>>> The water purveyor does the test at a cost of $600 plus the delay 
> >>>> waiting for it to get done.
> >>>> 
> >>>> We all know how things can evolve over time as people in different 
> >>>> positions come and go. Since 1991, up until now, the procedure was the 
> >>>> water purveyor provided the static pressure at the proposed job site. 
> >>>> This was the third party verification for the development of the 
> >>>> calculations by the installing contractor. 
> >>>> 
> >>>> Sent from my iPhone
> >>>> 
> >>>>>> On Nov 18, 2019, at 8:02 PM, Mark.Phelps via Sprinklerforum 
> >>>>>> <[email protected]> wrote:
> >>>>> 
> >>>>> Do you have to perform the test or do they do it?
> >>>>> 
> >>>>> Mark at Aero
> >>>>> 602 820-7894
> >>>>> 
> >>>>> Sent from my iPhone
> >>>>> 
> >>>>>> On Nov 18, 2019, at 8:57 PM, firstin--- via Sprinklerforum 
> >>>>>> <[email protected]> wrote:
> >>>>>> 
> >>>>>> Need advice on the best way  to fight a non required requirement. 
> >>>>>> Someone at the local water purveyor came up the the great idea to 
> >>>>>> require a full blown flow test for ALL proposed SFR fire sprinkler 
> >>>>>> systems at a cost of $600 each. The vast majority of water mains that 
> >>>>>> run down residential streets are 6”. There are a few 4” and that’s the 
> >>>>>> smallest. Who on Gods green earth thinks that two residential heads 
> >>>>>> flowing could over-run the municipal water supply, therefore, a flow 
> >>>>>> test is required to develop supply curve, really?
> >>>>>> Am I missing something or is this requirement BS and nothing but a 
> >>>>>> money grab? 
> >>>>>> Owen Evans
> >>>>>> 
> >>>>>> Sent from my iPhone
> >>>>>> _______________________________________________
> >>>>>> Sprinklerforum mailing list
> >>>>>> [email protected]
> >>>>>> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=iTziAtPF_lY685hJJ1vizDq1HKIibaCtX8p-L4yPSn0&s=RhKF9rf4aehsyLX_SomSwPubAxSKV3Vg9T4eFISBSDw&e=
> >>>>>>  
> >>>>> _______________________________________________
> >>>>> Sprinklerforum mailing list
> >>>>> [email protected]
> >>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> >>>> 
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>> 
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >> 
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > 
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to