These (there are 2 of them) are canopies over doors at a pre school that open 
up to the outdoor play area. The only thing under them that I am aware of are 2 
picnic tables under each. A 8.15.7.5 says that combustible furniture would not 
necessarily drive a need for sprinklers. I would also think that, given the 
occupancy, grills or other heating equipment would not be present.
  
  
  
 Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Apr 16, 2020 at 11:07 AM,  <Craig/GVL via Sprinklerforum Prahl 
> (mailto:sprinklerforum@lists.firesprinkler.org)>  wrote:
>   
>   
>                 
>   
>
>  What is the purpose of the canopies?    What’s going on underneath?    
> What’s the occupancy classification?
>
>   
>
>     
>
>   
>   
>
>  Craig Prahl    |Jacobs| Group Lead/SME – Fire Protection | 864.676.5252 |    
>   craig.pr...@jacobs.com (mailto:craig.pr...@jacobs.com)|www.jacobs.com 
> (http://www.jacobs.com/)
>
>   
>
>  1041 East Butler Road      Greenville, South Carolina    29606
>
>   
>   
>
>     
>
>   
>   
>   
>
>  From:   Sprinklerforum  <sprinklerforum-boun...@lists.firesprinkler.org>   
> On Behalf Of  John Denhardt via Sprinklerforum
>   Sent:  Thursday, April 16, 2020 10:52 AM
>   To:  sprinklerforum@lists.firesprinkler.org
>   Cc:  John Denhardt  <jdenha...@firesprinkler.org>; Matt Grise  
> <m...@afpsprink.com>
>   Subject:  [EXTERNAL] Re: Fabric canopies
>
>   
>   
>   
>
>   
>
>   
>
>  Fully agree with Matt.   
>
>   
>   
>
>     
>
>   
>   
>   
>
>  John
>
>   
>   
>
>  John August Denhardt, P.E.
>
>   
>   
>
>  Vice-President Engineering and Technical Services
>
>   
>   
>   
>
>  American Fire Sprinkler Association   
>
>   
>   
>   
>
>  301-343-1457
>
>   
>   
>   
>   
>
>   
>   
>   
>
>   
> >   
> >
> >  On Apr 16, 2020, at 10:14 AM, Matt Grise via Sprinklerforum  
> > <sprinklerforum@lists.firesprinkler.org 
> > (mailto:sprinklerforum@lists.firesprinkler.org)>  wrote:
> >
> >   
>   
>   
> >   
> >   
> >
> >  
> >
> >   
> >
> > The text says:
> >
> >   
> >
> >   
> >
> >   
> >
> > “…are constructed utilizing a noncombustible frame, limited combustibles, 
> > or fire retardant-treated wood with an inherently flame resistant fabric 
> > overlay as demonstrated by Test Method 2…”
> >
> >   
> >
> >   
> >
> >   
> >
> > It seems unlikely that it was the intent of the code language to separate 
> > the FRT wood from the other potential fabric support structures, but it 
> > could be read that way. If that was the argument, then someone would be 
> > saying that an aluminum frame was less fire safe than one made of FRT wood. 
> > That also seems unlikely.
> >
> >   
> >
> >   
> >
> >   
> >
> > My vote would be that the intent was to lump all of the cloth-covered-frame 
> > types together into a group of canopies that don’t need sprinklers…. But it 
> > would be pretty easy to request an interpretation and get a more 
> > authoritative opinion.
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> > Matt
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > From:  Sprinklerforum  <sprinklerforum-boun...@lists.firesprinkler.org 
> > (mailto:sprinklerforum-boun...@lists.firesprinkler.org)>   On Behalf Of  
> > Fpdcdesign via Sprinklerforum
> >   Sent:  Thursday, April 16, 2020 9:01 AM
> >   To:  Sprinklerforum  <sprinklerforum@lists.firesprinkler.org 
> > (mailto:sprinklerforum@lists.firesprinkler.org)>
> >   Cc:  Fpdcdesign  <fpdcdes...@gmail.com (mailto:fpdcdes...@gmail.com)>
> >   Subject:  Re: Fabric canopies
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >
> > Matt,
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > That version talks about fabric overlay on treated wood. This is just a 
> > pre-stretched fabric over an aluminum frame; no wood.   
> >
> >   
> >   
> >   
> >   
> >
> >
> >  Todd G Williams, PE
> >
> >   
> >   
> >
> > Fire Protection Design/Consulting
> >
> >   
> >   
> >   
> >
> > Stonington, CT
> >
> >   
> >   
> >   
> >
> > 860-535-2080 (tel:860-535-2080)   (ofc)
> >
> >   
> >   
> >   
> >
> > 860-554-7054 (tel:860-554-7054)     (fax)
> >
> >   
> >   
> >   
> >
> > 860-608-4559 (tel:860-608-4559)   (cell)
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >
> >   
> >   
> >   
> >   
> >
> >   
> > >   
> > >   
> > >
> > > On Apr 16, 2020 at 9:44 AM,  <Matt Grise via Sprinklerforum 
> > > (mailto:sprinklerforum@lists.firesprinkler.org)>  wrote:
> > >
> > >   
> > >   
> > >   
> > >
> > > NFPA 13 2016 8.15.7.2 discusses non-combustible frames covered with 
> > > inherently flame resistant fabric overlay.
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >
> > > Matt
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >   
> > >
> > > From:  Sprinklerforum  <sprinklerforum-boun...@lists.firesprinkler.org 
> > > (mailto:sprinklerforum-boun...@lists.firesprinkler.org)>   On Behalf Of  
> > > Fpdcdesign via Sprinklerforum
> > >   Sent:  Thursday, April 16, 2020 8:40 AM
> > >   To:  Sprinklerforum  <sprinklerforum@lists.firesprinkler.org 
> > > (mailto:sprinklerforum@lists.firesprinkler.org)>
> > >   Cc:  Fpdcdesign  <fpdcdes...@gmail.com (mailto:fpdcdes...@gmail.com)>
> > >   Subject:  Fabric canopies
> > >
> > >   
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >
> > > I am working on a building that has two 22 ft wide x 10 ft deep exterior 
> > > canopies. The construction is fire retardant fabric over an aluminum 
> > > frame. There is no storage underneath. NFPA 13 section 8.15.2.7 reference 
> > > omitting sprinklers where fire retardant wood is present, but mentions 
> > > nothing about any other fire retardant materials. The Handbook commentary 
> > > for that section mentions the general term “fire retardant materials”. 
> > > The obvious question is sprinklers or not?
> > >
> > >   
> > >   
> > >   
> > >   
> > >
> > >
> > >  Todd G Williams, PE
> > >
> > >   
> > >   
> > >
> > > Fire Protection Design/Consulting
> > >
> > >   
> > >   
> > >   
> > >
> > > Stonington, CT
> > >
> > >   
> > >   
> > >   
> > >
> > > 860-535-2080 (tel:860-535-2080)   (ofc)
> > >
> > >   
> > >   
> > >   
> > >
> > > 860-554-7054 (tel:860-554-7054)     (fax)
> > >
> > >   
> > >   
> > >   
> > >
> > > 860-608-4559 (tel:860-608-4559)   (cell)
> > >
> > >   
> > >   
> > >   
> > >   
> > >
> > > _______________________________________________ Sprinklerforum mailing 
> > > list  Sprinklerforum@lists.firesprinkler.org 
> > > (mailto:Sprinklerforum@lists.firesprinkler.org)    
> > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >  
> > > (https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-firesprinkler.org&c=E,1,h10_VhTFVKmQtgCy7zjn9IyC7gXFh4XDUAMLZpbx-A64f0Fe6KgqbwiAo7fzXwF3Lhsq8AXuAJ24GoWgqelBSHVRVqj8APMXXegMLTXZExMluXZIWDugCOhA&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!To-w0JkJncQQFdoRj98EVYEdp8nMlf1O1_b9AQSRYHzZYa2DLo5eN2un3LemCtWjqw$)
> > >
> > >   
> > >   
> >   
> >   
> >   
> >
> >  _______________________________________________
> >  Sprinklerforum mailing list
> >   Sprinklerforum@lists.firesprinkler.org 
> > (mailto:Sprinklerforum@lists.firesprinkler.org)
> >    
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >  
> > (https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!To-w0JkJncQQFdoRj98EVYEdp8nMlf1O1_b9AQSRYHzZYa2DLo5eN2un3LcTXt5zrA$)
> >
> >   
> >   
>   
>   
>   
>     
>  NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
>  _______________________________________________ Sprinklerforum mailing list 
> Sprinklerforum@lists.firesprinkler.org 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org  
>           
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to